Panelview550

vikkaraja

Member
Join Date
May 2004
Posts
37
Good Morning, This will be my first time trying to communicate with a HMI. I have a panelview 550 CAT 2711-B5A5 with a RS232 port. My question is what do I need as far as hardware like a cable to establish a communication using RSlink. I was told I should be able to communicate to this device with the followings that i have in my possession right now.... CAT1747-UIC. I tried and of corse it did not work for me. Please help. Thank you.
 
Hi Mickey thanks for the link. I tried it and guess what I see picture of the computer 1747-UIC and no panelview. What else am I missing or I am doing wrong.
 
If you can post a screen shot of your RSLinx configuration.
Tell us what cable your using between the UIC and the PV.
See Pic's below for examples.
Things to check: What comm port did the UIC take? See hi-lite on pictures. The cable is a straight thru cable. Pay close attention to the device type in RSLinx.

PVCable.jpg


RSLinxConfig.jpg
 
Good Morning Mickey,I am using a Allan Bradely Gray Cable with the following number AB96881501 from PV to CAT1747-UIC.And I am still seeing the seeing PV Icon on the screen.
 
I'm not familar with that cable number. Make sure its a straight thru cable. AB 2711-NC13 or any straight thru.
After that you might try a different station address in RSLinx. The PV will default to node 2 but it can be changed. Is this a new installation or existing? Do you have the PV's offline program to check its comm configuration or can you see the PV's configue screen?
 
Last edited:

Similar Topics

Hi guys. Just want to seek for some suggestion, I am having problem in communicating panelview 550 to my laptop so that I can upload the HMI...
Replies
1
Views
1,031
Dear team, I am trying to update the firmware of allenbradley panelview550 model 2711-K5A2 keypad type with previous firmware...
Replies
4
Views
1,900
I have 2 sister machines (builder from Germany closed years ago) that each has a SLC 5/04 and a Panelview 550 with a serial cable between them...
Replies
7
Views
2,231
Dear friends, I need your advice for a fault occurred in my HMI Allen-Bradely (panelview550) model:CAT 2711-B5A2. This fault is an alarm says ...
Replies
4
Views
1,713
Hello all, I am working on a project where I am converting SLC 5/04 PLCs to Compactlogix L32E. The existing panelviews are 2711-B5A8L1. I...
Replies
4
Views
1,302
Back
Top Bottom