Yeah, that won't work because as you see when the pressure switch opens, you get the alarm.
I'll try to show you the ladder here, but it's hard with formatting:
...MOTOR......OPS
---||---------|/|-----------TIMER 25Secs
...TIMER.DN
---||------------V2000
The rungs say if my motor is running and I don't see the OPS for 25 secs, then alarm.
This assumes that even during steady state you can withstand loss of pressure for 25 seconds. If you can't and need to immediately alarm once the pressure switch makes the first time, then you'll need to do the following instead:
...MOTOR
---||-------------------TIMER 25 Secs
...TIMER.DN.....OPS
---||-----------|/|----------V2000
This says that wait for 25 secs once the motor starts to even look at the OPS. If after 25 secs the OPS is not made, then alarm. Once the Motor stops, The Timer.DN bit goes low and you won't get the alarm.
Lastly, if you can withstand some time of no pressure during steady state running then you can modify the above like this:
...MOTOR
---||-------------------TIMER 25 Secs
...TIMER.DN.....OPS
---||-----------|/|----------TIMER2 5 Secs
...TIMER2.DN
---||-----------------V2000