Lost an output on a Micrologix 1500 the other day. Had several spares so I just re-assigned it. When I went to update the schematic, there was a note indicating that the same thing had been done about 3 years ago. The machine was roughly 4 years old at that point.

It's a relay output on a 1764-24BWA base driving a 24vdc, 5.4 watt, solenoid valve.

My first thought was that I should put a diode in to protect the contacts against the reverse voltage spike when the coil's magnetic field is collapsing, but I'm beginning to feel like this might be a plain ol' mechanical failure.

The valve can be cycled as many as 40 times a minute with a 450msec pulse. A rough estimate is 15 million cycles over the last 3 years.

What do you cats think?
 
You probably wore the poor PLC out. We use these (solenoids) all the time, at a much lesser rate, and haven't had a PLC falure.

An alternative is to add in a relay; it will relieve the PLC of most of the voltage, and make it last longer.
 
Had a similar situation but using relay outputs to drive solenoid coils(220V). These kept burning the relay contacts. Had a Scneider rep out and he advised using a ZBZ-VM supression unit directly across the solenoid coil. Viola problem gone. Maybe you can get a Sneider rep to source a low voltage unit. I did open one and it is just a MOV inside ( an expensive one..............)

Hope this helps
 
Yep, she just plain wore out I would think. A solid state output would be better with that duty cycle.
 
monkeyhead said:
My first thought was that I should put a diode in to protect the contacts against the reverse voltage spike when the coil's magnetic field is collapsing,

monkeyhead,

If you do decide to to this, be prepared for a difference in how the solenoid behaves. It will almost assuredly be of longer duration, even without changing any logic.

monkeyhead said:
I'm beginning to feel like this might be a plain ol' mechanical failure.

The valve can be cycled as many as 40 times a minute with a 450msec pulse. A rough estimate is 15 million cycles over the last 3 years.

What do you cats think?

15 million is between mechanical only cycles and electrical resistance load only (no inductive load) cycles of your typical relay. Acording to this Idec PDF.
http://www.idec.com/language/english/brochure/Relay_20Selection_20guide.pdf
Cycle wise you are a lot closer to the mechanical lifetime than the electical lifetime.
 
RDS said:
A 1N4004 diode across the solenoid coil will do it.
If you don't mind me asking, how do you calculate the size? It looks like this guy is rated for 1A/400V.

milldrone said:
If you do decide to to this, be prepared for a difference in how the solenoid behaves. It will almost assuredly be of longer duration, even without changing any logic.

because the induced voltage from the collapsing field is feeding the coil through the diode?

milldrone said:
Cycle wise you are a lot closer to the mechanical lifetime than the electical lifetime.

I suppose I could change to the base that has 6 FET outputs and 6 relays. Drive the solenoid with one of the FET and protect it with voltage supression.
 
I wouldnt drive a coil of this size direct from the PLC, there will always be suppression issues. Much better to have an interposing relay/SSR, which can be 'sacrificed' if anything goes wrong.

If you suppress the coil with a reverse connected diode then the 'off' time will be increased, probably by enough to upset your application if you are working at 40 times a minute.

Two ways round this:

Put a zener diode in series with the suppression diode, anything from 12 - 24v, this will allow the magnetic field to collapse quicker.

Overrate the interposing relay, and suppress the coil with a VDR, which will limit the voltage to a reasonable level
 
Since you're switching a relatively small current into an inductive load at a fairly rapid rate I'm with RDS and would also put in an interposing solid-state relay for maximum reliability. These normally have a flyback diode internally so all you would need is the relay+base. In addition, the switching time will be a little bit more repeatable (sticky or overloaded relays have caused me problems in the past) and consistent, although I have no idea whether it matters for your process ;)
 

Similar Topics

I've run into a non-plc issue that is proving hard to solve. I'm designing a mechanical device that has a base/foundation that must satisfy the...
Replies
3
Views
395
We have an existing VSD where a three phase circuit breaker feeds the drive, and two phases also tee off to a contactor, which is energised to...
Replies
12
Views
1,483
greetings to everyone. I want to learn big Mechanical presses like in the picture. Can you help me find documentation about this from...
Replies
11
Views
2,896
Hi all, This is actually a personal project, if that's ok. My uncle has some property that has a well, he wants to have the well automatically...
Replies
7
Views
2,485
Just curious how anyone else has controlled a VFD driven motor with a mechanical brake. I was using a PLC output to fire a brake relay while also...
Replies
19
Views
4,524
Back
Top Bottom