Mitsubishi E700 HMI

etong31

Member
Join Date
Jun 2008
Location
Kuala Lumpur
Posts
1
I am going to replace the above HMI.Do I need to reprogramme or just plug in ,power on and auto-load from the PLC and run like the Siemens S6 do ?
Is the Beijer E700 exactly the same as the Mitsubishi E700 HMI ?
 
Hi etong!

You are going to need the HMI backup, so you can download it with E-designer. You could upload the program from the panel you got today and download it to the new...

The Mitsubishi is beijers panel (the are developed by beijer).

Regards

/edmund
 