I have a question. I am in the process of commisioning some aditional programmuing and I/O to an existing system that NEEDS to be online monday.

The system is a dual 17 slot rack Controllogix (L56-L55) conected by a 1756-cnbr/d in each rack. I have added three modules to the remote rack - 2-1756-IA16's and a 1756-IA6I. I have the 1756-IA16's configured through RSLogix and operating with no problems. The issue is with the 1756-IA6I. I cannot get it configured. I get the error 'CODE 16 #6317 CONNECTION REQUEST ERROR CONNECTION NOT SCHEDULED'

My Controlnet experience is pretty limited and it has beeen a while. DO I NEED RSNETWORX TO CONFIGURE (SCHEDULE?) THIS DEVICE?? (the two IA16's did not) If so will the demo version of RSNETWORX work? (am currently SLOWLY downloading the demo @ my hotel) Could I just move the card to rack #1 without using RSNETWORX?

Any help would be greatly appreciated, as the client wants the equipment operation on Monday. (I just new everything was going to smooth up till this point!!)
 
Digital modules usially use Rack Optimized connection and adding digital modules not required re-scheduling

Analog module is always direct connection and you must schedule it
You need full version not a demo of rsnetworks to do it
Adding module to the local chassis should not require RSnetworks
 
Thanks Alot!!!!!!!!
You are a real life saver. I think I will justmove the module to Rack 1 and see about buying a copy of RSNetworx for future jobs (I have another dual rack job coming). I can now sleep easily (much needed - start up week) knowing that I can quickly resolve my only issue monday morning.
Just in case no one told you today Contr_Conn - YOU ARE THEN MAN!!!!!
 

Similar Topics

Hi all , Iam using 1756-IF 6I module for measuring voltage/currnet/frequency using transmitters. iam facing a clamping issue after 17mA. I...
Replies
0
Views
1,293
Hi, This is our first project with allen bradley kit. It seems using the ALARM_ANALOG and ALARM_DISCRETE data types with the ALMA and ALMD...
Replies
1
Views
2,963
I usually use the 1756-6CIS module because it is sourcing (can power a loop powered two wired device) but after reading the literature on the IF6I...
Replies
2
Views
1,661
Hi all I am a electrical engineer and I would like to know the how to wire a 2 wire tramsmitter ti 1756-If6I isolated analog input PLC module...
Replies
1
Views
2,911
Hi all I have a ControlLogix 1756-L71SP that i want to use for general PLC applications, not safety. I am running Studio5000 v33, i can't...
Replies
2
Views
58
Back
Top Bottom