I'm new here, so I hope I'm posting correctly. I'm using a Panelview Plus 1000 as an interface for two different systems (i.e. two ControLogix controllers). Is there any way I can write the active display number to BOTH controllers, and remotely change the display from BOTH controllers? I'm using Ethernet communication, and the only way I see it possible, is to assign tags to one controller, and use produced/consumed tags to send the information to the other controller. However, this will not work for me as the system may be run periodically with one controller powered off. Any suggestions?
 
Nope; Global Objects connect to only one controller.

I'm not sure how you could do Remote Display Number from two controllers. If Controller A is sending "10" and Controller B is sending "2", how would the PanelView decide which one to apply ?

Will one specific controller always be the one powered off, or is it a case of "either one" ?
 
I figured that was the case.

Controller "A" uses screens 2 thru 10, while controller "B" uses screens 11 thru 19 in my application. To avoid sending remote display change numbers to the HMI simultaneously from both controllers, I would simply write a zero in the display change register of the controller who's displays are not currently in use (i.e. if I am on screen 5, controller "A" is in use, and I write a zero to the remote display change register of controller "B"). That's why I needed to know if I could read the display number in two separate controllers.

In response to you last question, either controller can be powered off at any time (for maintenance).

Thanks.
 

Similar Topics

I have been working on this for a while now and I can't seem to get it. I was finally able to view the 1500 on the PanelView under the serial...
Replies
1
Views
15
I am working with a Micrologix 1400 and a PanelView plus Compact HMI. There are some HMI tags that are present in the HMI that is actively using...
Replies
11
Views
2,705
Hello . Info: Panelview plus 400 2711P-K4M20D Compactlogix 1769-l32E i make a program in RSlogix 5000 and Factorytalk view for...
Replies
9
Views
1,799
Anyone know how to build the communication between panelview plus 1000 and compactlogix l43s controller by ethernet. after downloading the program...
Replies
6
Views
1,303
Hello all. I have a question about communication between my HMI and processor. Somehow, one of our maintenance techs goofed up the program. We...
Replies
6
Views
1,907
Back
Top Bottom