hi all,

I have a machine that has a PC reading registers every 100ms from the PLC over MODBUS

is this ok ?

do you think it is a good idea to do so ? will this damage the serial port on the PC/PLC ?

thanks
 
Hi Farid,
One thing I think you should check is that your PC software is intelligent enough to make sure that it doesn't send the next Modbus request to the PLC before the PLC is finished replying to the last request. If the PC didn't respect this, it would get garbled messages I think, and have to re-try needlessly.
Other than that, as Dan commented earlier, if you or your customer actually needs this fast update, then by all means use it; it shouldn't slow down the PLC, as it probably doesn't give a high priortiy to replying to Modbus requests. I think rather that it would solve logic first, then devote any spare time to checking the Modbus port. Nor would it harm your PC, as today's PCs are much too quick to be burdened by mere serial communications.
Hope this helps,
Kind regards,
Roger.
 

Similar Topics

Dear All,, Our company wants an upgrade to existing PLC system; that involves in upgrading the scada system as well. I know there are well known...
Replies
6
Views
2,076
Hello people, I'm teaching a course to some students who already programmed plc's for about two years. So you can say they have had a fairly good...
Replies
38
Views
11,316
I'm looking forward Iconics. I had previously extensive experience with Citect and little bit less experience with Wonderware. Pros and cons with...
Replies
0
Views
842
It is rare that I ask for opinions. But here goes. Currently using a low cost NUC for an hmi. Looking for a low cost NUC or similar. thoughts
Replies
1
Views
1,166
In my project, I have created a UDT for VFD driven motor. The UDT has elements of .SpdCmd, .ManSpdCmd, .MinLim, .MaxLim among others. The idea...
Replies
1
Views
1,254
Back
Top Bottom