Slave To Slave Communication

engrselva

Member
Join Date
Dec 2007
Location
singapore
Posts
23
Hi GUYS
I have two PLC both of them S300 313C-2DP.
Both of them talking with each other through PROFIBUS
Now one HMI needs to be inserted in the PROFIBUS loop which then will talk TO SLAVE & MASTER PLCS. IS IT POSSIBLE TO DO THAT?


REGARDS
SELVA
 
Yes

It is possible to communicate two intelligent Slaves and you do this by configuring Direct Data excahnge from within you Hardware configuration.

I would suggest u use the Master PLC to collect all the Data from the Slave PLC's and communicate this to the HMI from the Master.

Rheinhardt

from Siemens Help File

Configuring Direct Data Exchange between PROFIBUS-DP Nodes

Introduction

In a configuration for direct data exchange (lateral communication), local input address areas of an intelligent DP slave or of a DP master are assigned to the input address areas of a PROFIBUS-DP partner.

The intelligent DP slave or the DP master uses these assigned input address areas to receive the input data that the PROFIBUS-DP partner sends to its DP master.

Number of PROFIBUS-DP Partner That Can Be Connected

The type of interface limits the total number of PROFIBUS-DP partners that are connected directly to a DP interface or are addressed over this interface by means of direct data exchange. A maximum of 32 PROFIBUS-DP partners can be addressed on the MPI/DP interface.

Applications

The following applications are possible for direct data exchange:
Starting Configuration
  1. Double-click the DP interface of the configured receiver (DP master or already configured I slave).

    Select the "Configuration" tab.

    To create new line in order to configure direct data exchange, click the "New" button.
  2. In the dialog that appears, select "DX" mode and assign the input address areas to each other (you can find more information in the online help for this dialog).


  • Mode: "DX" for direct data exchange, ("MS" for master-slave)

    Partner DP Addr.: PROFIBUS address of the DP partner

    Partner Addr.: Address of the logically assigned address area (sender)
  • Local Addr.: Address of the logically assigned address area (receiver)
 
RheinhardtP said:
It is possible to communicate two intelligent Slaves and you do this by configuring Direct Data excahnge from within you Hardware configuration.

I would suggest u use the Master PLC to collect all the Data from the Slave PLC's and communicate this to the HMI from the Master.

Rheinhardt

from Siemens Help File

Configuring Direct Data Exchange between PROFIBUS-DP Nodes

Introduction

In a configuration for direct data exchange (lateral communication), local input address areas of an intelligent DP slave or of a DP master are assigned to the input address areas of a PROFIBUS-DP partner.

The intelligent DP slave or the DP master uses these assigned input address areas to receive the input data that the PROFIBUS-DP partner sends to its DP master.

Number of PROFIBUS-DP Partner That Can Be Connected

The type of interface limits the total number of PROFIBUS-DP partners that are connected directly to a DP interface or are addressed over this interface by means of direct data exchange. A maximum of 32 PROFIBUS-DP partners can be addressed on the MPI/DP interface.

Applications

The following applications are possible for direct data exchange:
Starting Configuration
  1. Double-click the DP interface of the configured receiver (DP master or already configured I slave).

    Select the "Configuration" tab.

    To create new line in order to configure direct data exchange, click the "New" button.
  2. In the dialog that appears, select "DX" mode and assign the input address areas to each other (you can find more information in the online help for this dialog).


  • Mode: "DX" for direct data exchange, ("MS" for master-slave)

    Partner DP Addr.: PROFIBUS address of the DP partner

    Partner Addr.: Address of the logically assigned address area (sender)
  • Local Addr.: Address of the logically assigned address area (receiver)
Thanks bro RheinhardtP for the detailed explanation. I try and get back to you if there is a trouble.


selva
 

Similar Topics

CR3000 HMI ModBus TCP/IP Master has gotten erratic after increasing block size to 24 at DA70A in Protocol 1. What should a practical guide be for...
Replies
2
Views
559
hello i wanto asking the setting and program for communication modbus The plc that i use is CJ2m cpu31 i use extra communication module...
Replies
0
Views
1,703
Good morning, I am looking to establish a communication between one Profibus master and one Profibus slave. I downloaded the Profibus Master...
Replies
58
Views
14,471
I am using a Schneider M221 PLC. Is it possible to have 2 Modbus TCP/IP masters pulling information from the same slave? I have 3 plcs on the same...
Replies
3
Views
2,405
Hi all, What is the best way to set up a master/slave relationship with an S7-400 Master (Step 7 5.5) and S7-1500 Slave (TIA Portal) PLC? I could...
Replies
4
Views
4,577
Back
Top Bottom