I have a PanelView 300 # 2711-K3A2L1 that I need to connect to a Micrologix 1000 processor. I have an AIC Module but what cables do I need to go from the PanelView 300 to the AIC and from the AIC to the Processor?
 
Q19928 - 2711-NC21 and 2711-NC22 cables for the PanelView
Last Modified: 07/16/2002
Previously Released as #13911
The 2711-NC21 and NC22 cables are 9 pin to 8 pin mini-din cables designed originally to
connect a PV300 Keypad or a xxx5, xxx9 or xxx16 terminal directly to a ML1000, 1200 or
1500 processor.
They only differ by the length:
The NC21 is 16.4ft (5 meter)
The NC22 is 49 ft (15 meter)
The pinout of this cable is:
PV AIC+, ML1000
9 pin 8 pin (Rt. Angle)
DCD 1 -------- 5 DCD
TXD 2 -------- 4 RXD
RXD 3 -------- 7 TXD
GND 5 -------- 2 GND
4 ---|
6 ---|
RTS 7 -------- 3 RTS ; RTS/CTS are not crossed. They must be crossed when used with a
Belden network.
CTS 8 -------- 6 CTS
Problem:
The problem is when the NC21/NC22 is connected to an AIC+ and a Belden cable is also
connected. The handshaking pins are required in this setup and the handshaking pins not
crossed. They are required to be crossed for handshaking to occur with the Belden cable.
If Belden is not used, the handshaking pins are not required.
Alternatives:
Use a 1761-CBL-PM02 or a 2711-CBL-PM05 with a null modem adapter.
Or, add a 9 to 9 pin adapter to the NC21 cable with pins 7 and 8 crossed. But don't recross
pins 2 and 3, they are already crossed.
May 2002: New cables that correct the handshaking pins are available as Ser A Rev B.
Documentation
General Category: s EOI
Product(s): PanelView
Catalog #: 2711ND3
Series / Revision:
Subject
(Keyphrases):
Summary of
Technote
Information:
Documentation Technote: 2711-NC21 and 2711-NC22 cables for the PanelView Page 1 of 2
http://domino.automation.rockwell.com/applications/kb/RAKB.nsf/0/A4350EB6186504DF852... 6/29/2006
The new pinout of this cable is:
PV AIC+, ML1000
9 pin 8 pin (Rt. Angle)
DCD 1 -------- 5 DCD
TXD 2 -------- 4 RXD
RXD 3 -------- 7 TXD
GND 5 -------- 2 GND
4 ---|
6 ---|
RTS 7 -------- 6 CTS ; RTS/CTS are now crossed with a Ser A Rev B cable.
CTS 8 -------- 3 RTS
 
plgrooms said:
The PanelView 300 is a DH485 Model and does not have the 9pin port.

See picture below.
ForDH485Port.jpg
 
One more question, why can I not see the Panelview 300 in RSLinx when I connect to the AIC? I can see the SLC with no problems but the Panelview 300 drops out as soon as I plug in the laptop.
 

Similar Topics

I'm developing application for PanelView300 and one SLC 5/03 CPU. I've started with alarm list and noticed something strange. When I'm trying to...
Replies
1
Views
1,618
I purchased a PV300 with serial port and DH485 protocol (2711-T5A1 I think) by mistake. I wanted a PV300 with serial port and DF1 protocol. What...
Replies
14
Views
4,097
I am having pvc300 with me. I created my new program in ccw. The issue is that after clicking discover in ccw my hmi is not showing up there. Any...
Replies
0
Views
142
merry christmas and happy new year i have a click c0-00dr-d and allen bradley 2711c-t3m. can the panelview talk to the click plc via modbus...
Replies
1
Views
211
Is this the clock battery flat? Does anyone know how to remove the back of the PV 300 micro. Is it possible to replace this battery. AB says it's...
Replies
2
Views
1,145
Back
Top Bottom