Hi
I am struggling to get this to work (first time on this). I have folled the example on Kepwares driver help with no joy.

I have removed everyting from my plc rack apart from the ethernet module, and the lights flicker on the module when kepware is trying to read the data.

I have the comm.error light lit up on the module.

If I upload my PLC project is there anyone here who could take a peek?

Cheers
 
Hi again, made some headway, but the comms still fail when i run the kepware quick opc. I have created a single tag, D00005.

I have attached the latest PLC files and the kepware file for anyone who can give it a check over.

Cheers
 
Hi, I have experience using KEPServerEX to communicate with Mitsubishi plc, FX1S and FX2N. I'm using programming port for communication and so far it's working.

You can email KEPWare technical staff for further help. I did that too. They'll reply in a day.
 
Did you set the card up for TCP or UDP connections? for TCP you will need to configure error handling for the TCP Socket you are enableing for the server to connect to.

For UDP you do not have to do that.

The other important thinkg is to make sure you are using the latest version of the server and driver. There were changes made recently to improve operations.
 
hi cjd


is this your code? have you used special cards on Mitsubishi before?

first of all your card addressing and setup need to be done. the code attempts to use buffers for card starting at H6 (instruction "TO H6 K0 D100 K2" for example) which means that I/O for that card would have to be in same range (configuration shows 32 points which sounds right for this type of card. 32 points are 20hex or h20, in other words they are 0-31 or in hex 00..1F but since the start address is h60, that would be actually in X60-X7F, Y60-Y7F range).
Right after that there is a coil setting Y19. I don't see any I/O mapped to this plc and the way it's written this should be one of the Ethernet card I/Os (Y79 since h60+h19=h79).
 
Did a project recently with Q & Kep, could not get any joy with TCP, spoke to Kepware & they said UDP is the way to go.
You only one configuration in actual fact you don't even need that the one I have has melsec connections only (we ran in parallel with existing Scada).
 
Hi I have used he UDP protocol and revised my PLC file (latest in post # 3)

I have set all dip swiches as Kepware help. I have fitted the ethernet module to slot 6 of the CPU (header I/O starts at '90')

I suspect my PLC config is bad but the PLC goes into run.

Here is kepware help file sample code which i tried to copy, updating the header addresses and I/O to suit


1.png






2.png
 
All sorted. Kepware support did a fine job and told me that the final part of the device address should have been 255 instead of 1.

Thanks for everyones input



Cheers
 

Similar Topics

I have a strange Kepware issue I have been dealing with for a few weeks. I have Kepware setup with the Omron NJ Ethernet driver and reading in...
Replies
0
Views
97
Hi All, I am after some assistance setting up kepware to take tag data from an FX5U PLC, I have tried many many port numbers and still cant get a...
Replies
2
Views
157
Im trying to get data from AB guardlogix controller using Kepware in a remote location but it seems that version 6 can only support contrologix...
Replies
2
Views
440
Hi, Have anyone came across issue with Kepware or Linkmaster not returning correct values (Unknown Quality) for some tags From OPC DA Client...
Replies
7
Views
668
I’m attempting to configure KEPWare to poll a Modbus device via Modbus TCP/IP. However, everything I’ve tried results in an error being reported...
Replies
2
Views
410
Back
Top Bottom