hi all, I am using an SVA-2100 servo drive from automationdirect.com

it requires 3 phse 220 VAC power supply here we have 380, but single phase (phase + N) = 220 VAC and in the manual they say it accepts single phase supple, will it work if I connect 220 VAV phase and neutral to drive?

thanks ..
 
Farid said:
hi all, I am using an SVA-2100 servo drive from automationdirect.com

it requires 3 phse 220 VAC power supply here we have 380, but single phase (phase + N) = 220 VAC and in the manual they say it accepts single phase supple, will it work if I connect 220 VAV phase and neutral to drive?

thanks ..
you have to use step down transformer 380v to 220v than it will work
 
If you measured 220v across one leg and neutral, then yes it will work. We do that all the time to get 110v from 3-phase 208v.
 
HI kolyur, yes actually this is what I wanted to know..here power is 380 vc phase to phase and phase to Neutral 220VAC

servo driver SVA-2100 has five power inputs three four main power supply R S T and two for control circuitry...they say in manual that single phase conect 220VAc to R and S and and also to control circuitry... will a [pahse 220VAC and a neutral work ??

I have been using transformers for years now and it is very difficult to find one in here 3 phase 380 to 220 Vac

so I am hoping it works straight phas eand neutral


Cheers
 

Similar Topics

Hey All, I am looking to put a 1756-PA50 power supply in my application. I am having trouble finding any Rockwell documentation that specifies...
Replies
2
Views
2,707
Has anyone tried to parallel dc power supplies from different manufacturers. Specifically Sitop (Siemens) and Quint (Phoenix Contact). I've got...
Replies
10
Views
1,864
I have a 120ac to 24vdc 40amp power supply that went bad. Can I take two 120ac to 24vdc 20amps and put them in parallel? I know this works fine...
Replies
14
Views
5,634
I picked up a micrologix 1000 really cheap and it came with no cables. I can pickup one of the communication cable at a store nearby here. I...
Replies
9
Views
7,913
plz how can i determine spesfication of plc 24 v DC power supply as my power source 220v AC ? WHAT is its Current and volt .....etc
Replies
3
Views
2,605
Back
Top Bottom