fault in siemens vfd

mahamadreza

Member
Join Date
Jul 2006
Location
tabriz
Posts
17
dear sirs,
iwould like to inform you that we have asiemens midimaster vector drive type:6SE3224-2DJ5O ,22kw (MAX. 30kw); that drives a 18.5kw motor of cutter in aextruder machine. the distance between drive and motor is about 50m. newly it is tripping due to fault no:F101. according to operation instruction manual, F101 is related to "inernal inerface fault". we have not found any defective part or any disorder in software and only by switching off and on the fault removes for some hours and appears again.we have also checked grounding and cable sheild grounding. any help to improve this problem is highly appreciated.
best regard,
yazdanian
 
Check the I/O board. I've seen loose boards do this. Remove and re-install. Only powering off will reset this fault.


Nick
 
dear nick
Thank you for your reply. we checked the speed control signal 4-20mA and there was 25KHZ noise. by paralleling two 100pf and 1microfarad capacitors to that input we could improve the problem.
yazdanian
 
in the micromaster manual, it is mentioned: F0101 stack overflow, software error or processor failure.
i think this is caused by the following: when there is too much option boards or complex parmeterization, then the processor will not be able to do all the calculation in one scan.
try to reduce parameter p1800, this will relief the processor by increasing the scan cycle.
 

Similar Topics

I've got a SIMATIC HMI KTP1200 and hooking it up to PLC (s7-1200) for first time. On the HMI setup screen, it's asking me to enter: IP address...
Replies
5
Views
1,343
So, we have one servovalve that is very critical to machine operation and idea is (or was) to detect if valve gets disconnected from analog output...
Replies
11
Views
2,900
Hi We had a faulty DO card giving SF error in our Siemens PLC setup model 326-2BF01-0AB0 and we replaced this 326-2BF41-0AB0 I/O card. We updated...
Replies
4
Views
2,026
Hello Experts, I would like to seek advise on how or what tag i should use or do to get the PLC diagnostic buffer to know what is the root cause...
Replies
14
Views
5,628
Hello Everyone, I have siemens drive Cu310-2 At random Fault f.07453 happens, Any experience with this fault ? Could it be a bad encoder or...
Replies
5
Views
3,173
Back
Top Bottom