MadMaxx
Member
Greetings Everyone:
The system in question is a Compact Logix 5330 with (1) 24 VDC sink/source input module, (1) 24 VDC source output module, and (1) AC/DC out module.
The recurring problem we are having is that, on occasion, all the LED's on the 24 VDC source output module will go out at which point we lose all our outputs from our PLC, without the processor seeing this malfunction as a fault per se, amazingly enough.
It has been noticed that this problem has not recurred all that frequently since a ventilator fan was placed blowing across the PLC. However, we did take note that when the ventilator fan was moved away for cabinet maintenance, the problem with the output module manifested itself once again. So, excessive heat seems to be a instigating factor in this case.
Additionally, the procedure that is in use to 'reset' the PLC is to turn the processor key from run, to rem, to prg, then from prg, back to rem, and then back to run. We usually have to repeat this cycle with the processor key twice, at which point, the output LED's usually come back on almost in an instant thereafter.
Any suggestions that anyone may have for helping properly resolve the issues with this PLC would be greatly appreciated.
Thank you for your time.
Best regards,
Max
The system in question is a Compact Logix 5330 with (1) 24 VDC sink/source input module, (1) 24 VDC source output module, and (1) AC/DC out module.
The recurring problem we are having is that, on occasion, all the LED's on the 24 VDC source output module will go out at which point we lose all our outputs from our PLC, without the processor seeing this malfunction as a fault per se, amazingly enough.
It has been noticed that this problem has not recurred all that frequently since a ventilator fan was placed blowing across the PLC. However, we did take note that when the ventilator fan was moved away for cabinet maintenance, the problem with the output module manifested itself once again. So, excessive heat seems to be a instigating factor in this case.
Additionally, the procedure that is in use to 'reset' the PLC is to turn the processor key from run, to rem, to prg, then from prg, back to rem, and then back to run. We usually have to repeat this cycle with the processor key twice, at which point, the output LED's usually come back on almost in an instant thereafter.
Any suggestions that anyone may have for helping properly resolve the issues with this PLC would be greatly appreciated.
Thank you for your time.
Best regards,
Max