if i want to control an operation of a generator by PLC as when the main power supply is shut off , the generator must operate .


i want to make a delay time after the main power supply is shut off as the generator operate only after this delay time

it must add a timer delay to PLC , as the timers in PLC when the main power supply is shut off can not operate !!

the question now : can we make this function without add any external device ( timer delay ) to PLC ??

as we want to make this function without add any external device to PLC !!


thanks
 
magdyfayad said:
if i want to control an operation of a generator by PLC as when the main power supply is shut off , the generator must operate .


i want to make a delay time after the main power supply is shut off as the generator operate only after this delay time

it must add a timer delay to PLC , as the timers in PLC when the main power supply is shut off can not operate !!

the question now : can we make this function without add any external device ( timer delay ) to PLC ??

as we want to make this function without add any external device to PLC !!


thanks
I think you need to think about it a bit more to say the least.
Auto transfer switches, load monitoring and such.
What happens when the power comes back on?
Any generator will have its own controller, you could use it to detect a power outage and kick in the PLC timer. Since the generator has to be powered up and ready there's no need for a UPS and such.
More details would be great.
 
I think you need to talk to the folks at Cat or other makers of standby generation equipment. No point in you designing what they make in a package assembly.

Dan Bentler
 
leitmotif said:
I think you need to talk to the folks at Cat or other makers of standby generation equipment. No point in you designing what they make in a package assembly.

Dan Bentler
My thoughts exactly!!
I was being polite.
 
Mains / generator change over

I have recently worked on a DeviceNet System via a Hitachi EH-150 Processor, that provided signalling for interrupting Essential / Non essential supplies. Works very well. The only draw back is the system is very fragile when it comes to inclement weather as there is no lightning protection afforded.

Would this help you situation?
 

Similar Topics

hi, i have some question about the single phase line-to-line for the kinetix 2000. the manual only show that contractor using for the three phase...
Replies
0
Views
1,253
Hello. We want to buy a damaged metal detector, with damaged "main power board". Someone knows this construction and can tell anything about...
Replies
0
Views
1,132
Hello Everyone- I'm working on a new network deployment of AssetCentre and I am not able to authenticate with the application using our...
Replies
1
Views
400
TLDR: I try to establish the OPC communication between Kepware OPC DA Client to ABB 800xA OPC DA Server. In the Kepware OPC quick client of poll...
Replies
0
Views
850
Main rack contained power supply 140cps52400 and 140cpu43412A and RIO HEAD 140CRP93100 in addition to another I/o cards . Another remote rack...
Replies
8
Views
1,860
Back
Top Bottom