hi guys i have a f2-04thm temp card and i am trying to find out how to calabrate the card because the temps are up and down when at temperture can anyone help.
thanks stu
 
Calibration is done in software. Calibration is not the issue. If fluctuation is on the input, you have noise. Ground loop if T/C's are grounded. Use digital filtering. If the problem is output, your PID needs tuning. Use the built-in PID. It's easy to setup and works very well.
 
keithkyll said:
Calibration is done in software. Calibration is not the issue. If fluctuation is on the input, you have noise. Ground loop if T/C's are grounded. Use digital filtering. If the problem is output, your PID needs tuning. Use the built-in PID. It's easy to setup and works very well.

How do you tune the PID? i am neew to all this?
thanks
stu
 
Tuning PID is an art, and the subject of many books. Search this forum for a wealth of info.
The software has an Autotune feature. Do an Autotune, and it will set your PID values. Sometimes this is enough, sometimes you need to do some final tweaking.
 

Similar Topics

hi i have a problem on a machine it is controlled by a automation direct plc 205 with a touch screen(rsview 32) the problem i am having is the...
Replies
1
Views
3,615
Hello, I have an automation direct d2 262 plc and C-more HMI EA9T6CL-R. I need to prepare a program, scheduled to be performed on a future date. I...
Replies
1
Views
119
Hello all- I have a unique challenge using a customers Direct logic 06 PLC. This customer has a DC motor operating at 10 RPM which is turning a...
Replies
1
Views
136
Hi, I have been trying to run drive via Sysmac studio. I can ping the drive. I can see the logic bits going on/off as per command. But, drive is...
Replies
21
Views
563
Anyone tried Automation Directs new CM5 HMI. We've been the EA9's for a few years now with minimal complaints. A few failures here and there but...
Replies
17
Views
1,584
Back
Top Bottom