Hi guys,

I'm sizing up a redundant CLX setup using 1757-SRM modules. 2 CPU, 2 SRM modules, 2 racks, 2 p/s.
But I'm not sure if I should buy 1757-SRC1 x 1 unit or 2 units? As the SRM module has Tx & Rx (fiber optic cable). The 1757-SRC1 packages comes with 1 cable or 2 cables?
Please help.

Thanks a lot.
 
flyers said:
Hi guys,

I'm sizing up a redundant CLX setup using 1757-SRM modules. 2 CPU, 2 SRM modules, 2 racks, 2 p/s.
But I'm not sure if I should buy 1757-SRC1 x 1 unit or 2 units? As the SRM module has Tx & Rx (fiber optic cable). The 1757-SRC1 packages comes with 1 cable or 2 cables?
Please help.

Thanks a lot.
Isn't the "Dual" channel that determines actual system redundancy?
 
The 1757-SRC1 is just a fiber optic cable assembly with both the Tx and Rx fibers "zip-corded" together. Buy just one. You can also get an -SRC3 (3 meter) or -SRC10 (10 meter) if you are placing your reundant chassis in separate cabinets to protect against fire, flood, or collision damage.

The ControlLogix Redundancy System Manuals are absolutely necessary reading for any redundancy installation. There is a specific set of hardware and firmware that is tested and functional for each redundancy release of ControlLogix.

The current redundancy release documentation includes:

1756-RN650B
RSLogix 5000 v16.54 Enhanced Redundancy

1756-RN628G RSLogix 5000 v16.53 Redundancy
 
Ken Roach said:
The 1757-SRC1 is just a fiber optic cable assembly with both the Tx and Rx fibers "zip-corded" together. Buy just one. You can also get an -SRC3 (3 meter) or -SRC10 (10 meter) if you are placing your reundant chassis in separate cabinets to protect against fire, flood, or collision damage.

The ControlLogix Redundancy System Manuals are absolutely necessary reading for any redundancy installation. There is a specific set of hardware and firmware that is tested and functional for each redundancy release of ControlLogix.

The current redundancy release documentation includes:

1756-RN650B
RSLogix 5000 v16.54 Enhanced Redundancy

1756-RN628G RSLogix 5000 v16.53 Redundancy

Ken,

Thanks a lot for your info, appreciate it. I'll go thru the manuals as you recommended.
 

Similar Topics

Good Evening , We have a number of Powerflex 525 Drives . I took notice for years elsewhere and our plant , that our Powerflex 525 drive...
Replies
0
Views
638
Good Afternoon, Just wondering , are many of you using SAP in your plants ? If so , is it difficult to learn ? Are there many training...
Replies
10
Views
1,418
It better to have too many instead of not enough right?
Replies
26
Views
2,885
Hi all- I have an application where: - I have a fixed system with a pre-determined, static, network (say, 192.168.2.0/24). - That system...
Replies
13
Views
4,237
I have an application that needs 20 inputs and 20 outputs with only 10 XNOR and 10 NAND blocks. I could do it with relays, but this could end up...
Replies
16
Views
5,169
Back
Top Bottom