I'm having trouble getting communication with my SLC 5/05 using ethernet. I'm connected to the SLC ethernet port with a cross over cable to my laptop. The SLC 5/05 I.P. address is 100.100.100.101. My laptop I.P. address is set at 100.100.100.102 with a subnet mask of 250.250.250.0. The driver congured is the AB_ETH-1. am using RSLinx classic ver 2.51 I can't see the processor in RSLinx. When I try and go on line I get "No response from processor at selected path/node Diagnostics status failed Ox4" When i go to windows start/run/CMD I can ping the processor and it answers back. Can anybody see anything i've done wrong
 
When you created you Ethernet driver did you remember to put the PLC's IP address in "Station Mapping" in the Configuration? It is an easy step to miss. I will not go out and "Find" Ethernet devices you need to list them.

Good luck
 
Your subnet mask seems odd. I would expect it to be 255.255.255.0 Although if you can ping the SLC, that would point to the setup in RSLinx.
 
Thanks all of you.
now my system is communicating with my laptop, after mapping the IP address in channel configuration and changed the subnet mask to 255.255.255.0
 

Similar Topics

Hello I have a s7-1200 and I would like to read the tags present in this controller with my controllogix controller. The two controllers don't use...
Replies
4
Views
74
Can we use a Simotion D455 ethernet port x127 as a gate, to access S7-1500 plc Tia Portal program ? In the Simatic manager, we used Netpro to do...
Replies
2
Views
84
So I have a sort of unique situation where I'm wanting to run a PF755 from the IO and over ethernet. Of course, this comes with it's own set of...
Replies
9
Views
259
Hi all, My ethernet port on my laptop recently broke and I was hoping to just use a usb-c dongle in the mean time to go live on my PLC until I...
Replies
14
Views
453
Hi; In a cabinet of a machine, a Fatek PLC with an Ethernet communication card is working. In the same cabinet, there is a 1 kW inverter. When...
Replies
16
Views
499
Back
Top Bottom