monitoring multiple rslinx opc/dde nodes in rsview32

dereks

Member
Join Date
Sep 2008
Location
Wyoming
Posts
3
I am trying to monitor coms from multiple rslinx opc/dde nodes in rsview32. I have tried different ways to accomplish this, to no avail. I assume it should be possible, since linx is also a rockwell product and you can visually monitor nodes in linx (rswho). Any thoughts would be appreciated.
 
RSView32 can be connected to multiple OPC/DDE server, unless you have RSLinx Lite (no OPC support) or RSLinx Single Node (only one node :cool: ).

You may check for the RSLinx Activation you have looking at the title bar, when RSLinx is opened.

When you say you cannot get this work, what do you exactly mean ?
Did you get errors?
Also could be useful to know the software version you use, the network and the PLCs connected to it.

- [font=comic sans ms,sans-serif]fuzzy logic[/font]
 
To what types of devices are you connecting? PLC/SLC/Logix?
And what I/O Server?
RSLinx supports several predefined internal status items that can examine each topic for info about the attached processor.
For Logix, I know it supports an "@IsPresent" item, but I don't remember if that works with PLC/SLC. Can try it I guess.

Check the help in RSLinx (if using that). Search for "Predefined"
 
thanks for the help, i'm playimg with the "@IsPressent" thing right now i also found a "Comm_Err('Tag')" That seems to do the trick.
 

Similar Topics

Hi, I would like some help in figuring out (1) how to monitor communications between a PanelView and multiple PLCs, and (2) what to do, if a PLC...
Replies
1
Views
2,181
Hi, I´m doing my first application in Citect. This application is a simple digital inputs (almost 70 tags) monitoring application and writing this...
Replies
1
Views
4,070
Hello everyone! I need to connect to a DL205-1 CPU and, as far as I know, I need to use DirectSOFT 6 software for the connection. Is anyone...
Replies
1
Views
62
Our punch press has a SLC500 with HELM weight module (HM-604-WM) for tonnage monitoring. The operator enters the weight range on the HMI, which is...
Replies
9
Views
201
Hello, I have been trying to figure out how to connect to and monitor a DLR that is on a remote rack from my PLC. The local has a 1756-L81E and...
Replies
0
Views
117
Back
Top Bottom