Working on a project where I need to link 3 Rice Lake 520 scales to a 5/03.The scale units are designed to do AB remote I/O by setting dip switches.Starting simple I would just like to be able to view (in the program) what ever the scale indicator is showing. I looked over the 1747-SN manual and I don't quite under stand 1/2 rack-1/4 rack full rack? Any advice to get me started on the right foot will be appreciated.
Terry
 
I'm not familiar with the 520i indicator but if its similar to the 92I indicator you can get optional cards in this case an analog output card. Its too bad you want to go to a single 503 as you can transmit via ascii from the indicators I usually use the ascii from the indicator constant transmit CR LF on all my indicators with the exception of the one hooked up to the 920I indicator. Not sure on the rack thing so I will refrain from my immediate assumption that being the available room left on the 503 backplane
 
The rack size is the amount of I/O information being passed between the scanner (SN card) and the adapter (scale card). The scale card should specify what rack size each should be set at.
 
I appreciate all the help. Finally found out what I needed to know. The scales use 2 words. 1st word is the scale weigh data. To see a -scale weight you have to multiply the input data by -1.0 when bit 4 of the 2nd input word goes high.

Thanks to all
 
Terry Boblitt said:
I appreciate all the help. Finally found out what I needed to know. The scales use 2 words. 1st word is the scale weigh data. To see a -scale weight you have to multiply the input data by -1.0 when bit 4 of the 2nd input word goes high.

Thanks to all

1747-SN with 5 scales on RIO

sn_scales.jpg
 

Similar Topics

We are in the process of upgrading a controls system. The existing system is a SLC500 with some IO cards and a 1747-SDN module communicating to a...
Replies
5
Views
529
se me desprendieron los cables del cable usb quiero soldarlos pero no se como van los cables si alquien me pudiera proporcionar una foto o como...
Replies
1
Views
385
Hello, I've got a project where I need to get information from two ABB ACS880 VFDs onto the plant operator's screen (or alternatively, onto...
Replies
23
Views
2,572
Hi Newbie here :yeah: Can one of you experts help me with setting up a simple BTR and BTW to just test 4 analogue inputs 4-20ma (1974-if4i)...
Replies
11
Views
989
Hey guys, Setting up my new laptop on windows 11. Got all my software working in Ethernet/IP. Now i'm trying to connect into older PLC running...
Replies
10
Views
1,335
Back
Top Bottom