For an Allen Bradley PowerFlex 4, what is the correct setting for P033 (Motor Overload current)? Is it the Motor Name Plate current, or is it Motor NP current times Service factor, or is it Motor NP current times 1.5 or something else?

A drive specialist told me to use Motor NP current times 1.5 which seems high to me.

This is for a small 480VAC, 0.5 and 1HP drives.
 
Set it to the motor FLA. The drive takes care of the 150% for you. They should call it Motor Nameplate Amps, because that is what you should enter. If the curent exceeds 150% of your P033 setting for 60 seconds, or 200% for 3 seconds, the drive will fault for "Overload".

There are other paramters in which you can derate the motor, or set an instantaneous current trip point.
Paul
 
OkiePC said:
Set it to the motor FLA. The drive takes care of the 150% for you. They should call it Motor Nameplate Amps, because that is what you should enter. If the curent exceeds 150% of your P033 setting for 60 seconds, or 200% for 3 seconds, the drive will fault for "Overload".

There are other paramters in which you can derate the motor, or set an instantaneous current trip point.
Paul
Agree with okie.
FLA is what we use.
Derating can be done by setting up a couple more parameters in the drive, did not have to use any so far.(A089 and one more, not sure which one, check the manual).
 
to clarify, FLA is the nameplate amps x 125%, or NPA x 1.25 = FLA

of course, if the nameplate states FLA,. then this calculation isn't needed
 
No, OkiePC has it right. Enter nameplate amps. The drive uses this value to do the thermal overload protection and, on PWM power the service factor is always 1.0. This is not the same as figuring heaters for an overload block.
 

Similar Topics

Im trying to diagnose a loud vibrating/humming noise coming from my companies Kollmorgen Cartride Direct-Drive Rotary motor. The motor is being...
Replies
4
Views
602
Hi all, I have a powerflex 525 where there is no voltage coming out to the motor. The drive was reset to factory defaults with stop and saftey...
Replies
13
Views
2,754
Hi All, I have been asked to commission two new Powerflex 525 vfds on site which I've never done before and I've ran into a problem which I'm...
Replies
3
Views
1,394
I've got motor that ran fine for years, but now it's sarting to overshoot its target position a few times a day. Is this indicative of a motor...
Replies
24
Views
5,743
Hi all, I have a Powerflex 40 controlled by a 1769-L24ER, when VFD parameter P036 is 0, motor starts and stops normal but when parameter is...
Replies
6
Views
1,924
Back
Top Bottom