Communication with PV1000

randy

Supporting Member
Join Date
Apr 2002
Posts
158
I am experiencing problem with communication to a PanelView 1000 CAT 2711-AT-T10C9. I am using the DF1 Point-to-Point Transfer using the standard RS-232 Cable.



I have no problem with communication with the PanelView 300. The baud rate that I have the 1000 terminal set at is 19200, which is the specified setting. Also, I am using PanelBuider32 Ver.03.81

Something that I am over looking?


Thanks



rmonroe
 
randy, your catalog number indicate a DH-485 Panelview... the port is RS-232, but protocol isn't DF1.

You have to setup the use of RSLinx (configured as DH-485) driver from Panelbuilder32 download options.

Have a look to the post in the link, it is a similar case; there you may find some infos about connection and settings.

LINK

Hope this helps....

- [font=comic sans ms,sans-serif]fuzzy logic[/font]
 
Last edited:
just got back from a quick vacation with the wife...thanks for the information.

rmonroe
 
Randy
Visit follwoing link.
http://www.ab.com/en/epub/catalogs/12762/2181376/1239781/1670480/1681260/tab7.html
it mentions that 2711-T10C9 has Two RS232 ports
one with RS485 protocol
Another for Printer only.
"
" *Terminals with DH-485 communications require application file uploads/downloads through the communication port. The RS-232 printer port on these terminals is for printing only."

You need to configure DH485 Driver for the Com port of your programming terminal in PanelBuilder 32 software.

You may test communication in RSLinx, by configuring the DH485 driver for the PV.

Good Luck!
Thanks
- Makarand
 

Similar Topics

In my case I was having panelview900 connected to SLC 5/03 through DH485 using AIC+ Advanced Interface Converter (1761-NET-AIC), an Isolated Link...
Replies
1
Views
1,813
Ok, so I'm trying to set up a system to play around with and get some programming practice in. I've got an SLC5/04 connected to the computer using...
Replies
4
Views
1,931
Hey guys, I'm in school and our controls lab just recieved a PV1000 and a bunch of DeviceNet equipment. We have RSLinx and PanelBuilder32. Since...
Replies
2
Views
2,723
I have created a project in TIA Portal v16 Upd6 with S7-1200 (6ES7214-1AG40-0XB0) and WinCC Unified (PC station). The communication between the...
Replies
4
Views
137
Hello We have installed several G.E. Fanuc 90 70 PLC Everything was ok but suddenly we can not communicate anymore with any PLC with the software...
Replies
0
Views
64
Back
Top Bottom