Jeebs said:
Weird. Our panels do revert to default setting.
No they won't, test it if you like but they sure won't. I just talked to the Siemens hotline and apparantly al graphic lists keep their value beceause in chemical plants, this is required, bit of strange axplanation I think.
Jeebs said:
System alarms setup on our panels, which can show me errors from over 3 months ago:
General > Display > Select alarms and tick both pending and unacknowledged. (not that it really matters for system alarms)
Right next to it we have selected only System.
So basically we have a alarm window only for system alarms.
With this setup we have a buffer of several months.
Think we created a separate window just because they disappeared within 2 secs......
You could also log the system alarms and then display the log. For logging check the Alarm Classes page.
I want it to apear in the current alarm list, so this isn't a good solution for me.
JesperMP said:
This is what you are looking for:
http://support.automation.siemens.com/WW/view/en/19687561
Notice, the effect will be the same if the CPU is in STOP as that the connection is lost. You can use it to display a message saying "Connection lost, or PLC CPU is in STOP".
That's exactly what I need.
Outrageous that you have to pay to get the exact solution.
I'm now testing a script I wrote myself, no need for the time too. Just use the internal clock memory.
Only thing I hate, is that the fastest way to detect an error is 1 minute beceause you can't call a script faster than that.
I now have 2 scipts. 1 is called by a tag from the plc (clock meory from plc, bit changes every second, called upon change) to increase an internal integer value.
The second script compares the counted value with the copy of the counted value (counted value is copied at the end of this script), when they are equal, there's no comm.
Still has an error in it, but I beleive it will work (only a bit slow)
Thans for the help you guys.