Hi, Has anyone had the problem with all 4 channels maxed out to 32767, even with the wiring terminal unplugged. Tried changing NI4 Card, no joy, moved NI4 into different pos in rack, no joy. Measured inputs, (Current) All good, not floating high above ground. Thinking maybe rack or PSU???? Any ideas???
 
Did you check the switch settings on the module? Each channel has the choice of being a current or voltage input. Try using a voltage setup, and use a volt meter to confirm that a voltage of what you expect is applied to the channel's IN+ and IN- inputs. I'm not sure how you would verify with current inputs unless you had another instrument to compare with.
 
You can verify the input signals without lifting wires by measuring voltage at each input channel. It should be 1-5 vdc for a 4-20ma current signal (250 Ohm internal resistor).
 
Has it ever worked? If it's a new system and is still being commissioned, it still could be a configuration problem. Is the NI4 in a local rack or a remote rack?

If it is something that used to work, what happened just before it stopped working? I wouldn't suspect the rack if everything else in the rack is working.
 

Similar Topics

I would be very grateful if someone could give me some guidance with a problem i have. I am trying to swap a 1746-NI8 which had failed for a...
Replies
8
Views
4,471
Can't seem to find any manuals depicting programming M file and any other info for installing the NI4 analog Input card. SLC5/04 card is going in...
Replies
1
Views
1,866
Hey guys, I need to do a 0-10vdc to 4-20ma conversion using an allen-bradley NI4 analog card can anyone help I have to give an analog output to a...
Replies
5
Views
2,661
Maybe someone in this forum has encountered this and could offer some suggestion. We connected a 1746-NI4 via 1747-ASB to a PLC5/80 on Ch1B...
Replies
13
Views
5,472
I’m attempting to send a temperature from a SLC-5/02 to an EZiMarquee display. The vendor said to use a MSG instruction to send the data to the...
Replies
1
Views
81
Back
Top Bottom