Hi all

I`ve got 2 masters (S7 315-2DP, S7 316-2DP) on profibus, each with his own slave (also on the same profibus).
How can exchange data between the 2 masters?
Do i need special FB`s?

greetz
Tonny
 
Last edited:
Hello Tonny;

The easiest way, as long as the information exchanged between the masters is limited to 244 words Out/In would be to use a DP/DP coupler:
http://support.automation.siemens.com/WW/view/en/1179382

This is a slave with 2 DP interfaces (and addresses), one for each master. You configure one interface as a slave to DP-master1, the other as slave to DP-master2, and whatever DP- master1 writes to his slave can be read by DP-master2 (also vice-versa).

There are other ways to do this, butr they requires either additional CPs, and programming. The DP/DP coupler is really the simplest configuration possible between 2 DP-masters.

Hope this helps,
Daniel Chartier
 

Similar Topics

Hello Guys, I'm trying to program S7 200 CPU 212 using USB/PPI mm ( 6ES7 901-3DB30 - 0XA0 ). Uploading the program from PLC is good but when I am...
Replies
2
Views
2,014
Hello. Is it possible to communicate with one wago module (slave on profibus) or ET 200 from two different siemens controllers (both masters)? Thanks.
Replies
7
Views
2,210
Hallo sir, Can some help me regarding following doublts? I have one rs-232 ppi multimaster cable of s7-200 plc.On PC side on RS-232 D type...
Replies
2
Views
7,084
Hallo sir, Can some help me regarding following doublts? I have one rs-232 ppi multimaster cable of s7-200 plc.On PC side on RS-232 D type...
Replies
1
Views
2,247
I am a student in the faculty of engineering and in our project we use siemens PLc s7-200 cpu222 and wincc flexible 2005. we want a schematic...
Replies
1
Views
3,982
Back
Top Bottom