Wago 750-343

If I understand you correctly. You are using a Wago module for I/O on a Siemens S7 PLC. No you can't tell from looking at the modules. All addresses are setup in the hardware configuration of the project in Step 7.
 
CharlesM said:
If I understand you correctly. You are using a Wago module for I/O on a Siemens S7 PLC. No you can't tell from looking at the modules. All addresses are setup in the hardware configuration of the project in Step 7.

Is there a way to tell the location of the addresses of the inputs and outputs on the WAGO by cross referencing the hardware configuration, or would the only way to know the address be to cross reference wire numbers to schematics? It just seems like there would have to be a way to know what physical inputs and outputs on the WAGO correspond in the program.
 
So you know what they are in the hardware config. but your
trying to find where they are used in the program???
 
In the hardware config you put in all the modules in the i/o rack. The module determines how many addresses are used. I think by default Step 7 will start at the first input address I0.0 and first output Q0.0. However you can put any address you want.
 
CharlesM said:
In the hardware config you put in all the modules in the i/o rack. The module determines how many addresses are used. I think by default Step 7 will start at the first input address I0.0 and first output Q0.0. However you can put any address you want.

Thanks Charles for the help.
 

Similar Topics

Is there a way to know internal addresses of inputs and outputs by looking at the WAGO module wiring and lights?
Replies
2
Views
2,289
Hello, I am in possession of a WAGO PFC 200 750-8216 which I was successfully able to set up as a Modbus RTU Master to a slave device using...
Replies
0
Views
72
I have a project to setup base programs across multiple PLC platforms that can be used for Modbus communications to various sensors that have...
Replies
0
Views
113
Hello, I m having a problem with wago 750-862 plc. The plc won't start automatically in run mode after a power reboot. I've also tried the...
Replies
4
Views
337
Hello everyone, I am trying to setup a Wago 750-8100 PLC to send a text message out via ethernet port, if I get a Digital input that is true. I...
Replies
0
Views
341
Back
Top Bottom