Hi All,

I have an AllenBradley Flex IO 1794 IB16, which is a non isolated 16 channel digital input.

I want to control a VSD and a DOL motor.

What I am intending to do, is to connect first 3 channels, so that the DI card sources the +24V DC.

For the rest of the channels, I want the VSD's control card to source the +24V DC.

I would connect both the VSD and the DI card's neutrals together. Would this work? Please refer to the attached schematic.

diq.jpg


Thanks
 
I'm surprised that your VSD doesn't have dry contact outputs to take to your input card? That way you don't have to worry about input voltage. Can you give more information on yoru VSD and it's outputs to the input card? I'd be more inclined to have the VSD fire isolation relays and take the relay contacts back to the input card instead of tying the DC commons together.
 
Thanks for the instant response.. Much appreciated...


Yes, the drive does have relay outputs and they have been used for a different purpose.
The drive's 24VDC is used to for controlling the pushbutton start stop, etc and lot of wiring has been done already and I just didn't want to do a whole lot of rewiring. ( this is talking about 10 drive motor combinations).

this digital input ( Sourced from PLC ) is a new modification and I thought I could add it, without disrupting the existing system. Would this cause any issues?

thanks and regards
rvim002
 
It should work if you have the commons tied together. Typically my 24vdc common is tied to ground as well. It's not an ideal way to do it but it should work for you.
 

Similar Topics

Good evening everyone! This is my first post here, after extensive searching on the net I couldn't find an answer to my question so I thought I...
Replies
1
Views
3,480
HI, Hopefully someone can point me in the right direction, the problem im having is with a direct logic 205 PLC DL260 CPU. The PLC in running a...
Replies
2
Views
4,149
Hello, I would like to change the way we currently login to our PanelView Plus terminals. Currently we use the standard terminal features, Logon...
Replies
6
Views
3,311
Good day all. I have a bit of a problem with one of my digital input module, I think. In the attached ladder (Ladder 20, Rung 29) there is an XIO...
Replies
6
Views
3,226
Order number is 6ES5420-8MA11 in S5-100U Plc.This is non-floating digital input module.What is the equivalent of this module in S7-300?And what is...
Replies
0
Views
2,189
Back
Top Bottom