We are trying to communicate directly to the PV900 with an RS232 comm port, using our laptop. We are using RSLinx and Panel Builder 32. We have a lot of different cables and we also have a PIC module. We need help configuring everything.
 
You have a DH485 protocol PV. You will need to use the 1747-PIC/AIC+ driver in RSLinx. You have to have a real serial port to use this driver.
Cable needed is a straight thru.
If you don't have a real serial port on your laptop then a 1747-UIC ( USB to DH485 converter) would be your best bet.
 
Thanks Mickey. When you say "a true serial port", do you mean a 9-pin "D" connector on the back of my laptop? Or can I use a USB to 9-pin "D" cable?
 

Similar Topics

Hi All, I have two PV900 I would like to swap, ones screen is dead/dying. from Ser-F Rev C(dying screen) >to> Ser-D Rev S obviously the PVA cant...
Replies
9
Views
2,708
Hello! I am working on setting up a PanelView900 to work with a machine using a SLC5/03. The PV900 only has Ethernet and DH485 ports, so I assume...
Replies
20
Views
7,324
Hey All. I am having an issue with an old PV900 Standard. The part number is 2711-T9C9. The first issue is that on powerup the screen is sittting...
Replies
9
Views
2,604
Iam having a problem tracking down a fault on a machine. The problem is with a separator controlled by a SLC500 (1747 L542B 5/04), this has a...
Replies
1
Views
2,513
The problem started with an error 208 in my PV900 after a program change and download to my slc 5/04. The logic had worked for over 2 years...
Replies
2
Views
2,766
Back
Top Bottom