Data Links in RSLogix 5000 Ver.16

Automation1

Member
Join Date
Jul 2007
Location
Minnesota
Posts
21
If you define a data link for a drive that is type Dint, do you have to leave the next open field undefined? Is each data link field only a word?



Thanks in advance.
 
Which drive and which network are you using ? And which versino of RSLogix 5000 (v16 has significant changes in this regard).

Ordinary DataLinks for 16-bit drives (1336+, PF70, etc) have two 16-bit words (A1, A2, B1, B2, C1, C2) per DataLink so you can transfer two parameters per enabled DataLink.

When you use a 32-bit drive like the 700VC or 700S, you only get the choice of A, B, C, D. You don't have to leave any spaces or skip any DataLinks.
 
V16.03.00 (CPR 9)

I am setting up the following drives on a ControlNet network:
1336E Impact
1336 Plus
PowerFlex 700 Vector


If we look at the PowerFlex 700 and I set up DataLink A. DataLink A has two fields in which I can define parameters. What if the two fields I define are type Dint for just DataLink A?

Thank you.
 
I might have to eat my words on that one.... I haven't used 32-bit DataLinks in a while. I'm going to do a little research.
 
Ignore my previous statements, because they are incorrect.

Here's the sanity check: Knowbase Answer ID # 24072.

On a PowerFlex 700 Vector Control drive, a DataLink is 8 bytes: 2 x 32-bit parameters.

So fill in both DataLink A1 and A2 (and B1,B2,C1,C2,D1,D2) with parameter numbers in each one. The I/O connection will be properly sized to fit the 32-bit DataLinks.
 

Similar Topics

Hello I have a s7-1200 and I would like to read the tags present in this controller with my controllogix controller. The two controllers don't use...
Replies
3
Views
36
Hi folks, I'm not as accustom with Siemens & WinCC, however I've been asked to increase the amount of data an existing application is logging...
Replies
2
Views
65
Has anyone migrated Proficy Historian data to a new server? I followed the guide to move all the data over, but when I run the utility, it stops...
Replies
0
Views
45
I cannot add SLC500 analog input tag (I: 8.3) to EZSeries Touch Panel Editor (V 5.3). I used all the listed tag datatype but it all says "Invalid...
Replies
10
Views
257
Hi, Wy we log data in PLC using DLG instruction, when we have option to log data in HMI
Replies
1
Views
78
Back
Top Bottom