What data function shall i use to set the limit

Actually i want my value not to start from ZERO

which seems to be better option shall i limit the values like lower and upper limit or use some other data function becasue it seems to be quiet messy
 
Thanks guys for considering it...
bkottaras mate i have use compare function but on the output i used N22:0 that was the spare bitt which i was assuming to use in the later data function as an input but when i execute it i get an eroor
Address Must be specified to the Bit Level.

whats this ...could uu Plz
cheers
 
That means that you were trying to compare a bit with an integer. N22:0 is an integer value. N22:0/0 is a bit...

Use a COMPARE if EQUAL or LESS
If true then MOVE current value to Minimum Limit
Flip that.

If true then MOV Minimum Limit to current value. Otherwise, you'll adjust your lower limit and not limit anything.
 
OZEE said:
That means that you were trying to compare a bit with an integer. N22:0 is an integer value. N22:0/0 is a bit...


Flip that.

If true then MOV Minimum Limit to current value. Otherwise, you'll adjust your lower limit and not limit anything.
Agree.
As OZEE said, you are eddressing a whole word instead of a bit by using N22:0.
N22:0/0 or N22:0/1 are bits.
Use one of the bits for your application.
Just make sure nothing is written to N22:0 also from another location (I've been bitten by this one a long time ago)
 

Similar Topics

Hello, I have a motor that we are sending a RPM Speed Output from 0-100% to the VFD. However, the Motor HP needs to be limited to 6000 HP and the...
Replies
3
Views
88
Hello, I have a quick question. I have been using scripts to change the color of buttons. The reason, I am usually using multiple hmiruntime.tags...
Replies
1
Views
99
Good evening all! I hope you folks are doing alright today, as I've got a situation that I believe I've come up with a solution to but I wanted to...
Replies
1
Views
436
Dear Experts, I'm just started working with GEO SCADA and I need your valuable help. Currently, I'm trying to edit the alarm limits on MIMIC...
Replies
0
Views
209
Possible dumb question here, but how does running a motor through a gearbox effect a VFDs ability to limit the torque on the driven load? My gut...
Replies
2
Views
522
Back
Top Bottom