Hi all, I set 1756-IF16 Analog input card's input range to 0 ~ 20 mA. 20 mA is equal to 20000 Engineering unit. Is it possible to get input more than 20000 in case the mA is 21 mA. Thanks a lot.
 
The input scaling simply defines what engineering unit (EU) should represent 0mA and what EU should represent 20mA. If the signal goes beyond 20mA, then your value will continue above the 20000 you defined for 20mA. Likewise if you defined 4mA as 0 (EU) then if your signal dropped below 4mA then your EU would be a negative value.

The module you are using is capable of detecting a signal from 0 - 20.58mA.

OG
 
In addition, the out of range bits are not set at the 4ma and 20ma like the 1771-IFE. They are actually at 0 and 20.58.
 

Similar Topics

We have L72 controller of Rockwell make with 4 nos. analog inputs from pressure transmitters. Due to break in cable connection OR transmitter...
Replies
7
Views
2,026
Hi everybody, I inherited a redundant 1756-L71 ControlLogix system with 2 racks with some DI, DO, and AI redundant modules (1715 series). The...
Replies
6
Views
2,360
Dear all, I a have issue with 1756-IF8 Module , I reading some Air pressure and temperature analog values from this card , I have total 4 Analog...
Replies
7
Views
2,664
Is there a way to see what the actual field signal value is going into each channel of the Analog Input I/O card 1756-IF16? In other words, I...
Replies
4
Views
3,594
Hi, I have just powered up my ControlLogix PLC with analog input 1756-IF16H. Two of the module shows an indicator: -Cal flashing green -OK...
Replies
1
Views
2,529
Back
Top Bottom