Danfoss FC302 DATA-LOGGING

recycled_mind

Member
Join Date
May 2007
Location
Cebu, Philippines
Posts
118
Hello everyone,

I have just finished installing two units of 30KW Danfoss FC302 VFD for chain conveyor applications. Now, my client wants to log all the errors, faults, and alarms of the VFD, specifying the time and date of each errors, fault and alarms.

Can anyone suggest of a cost effective way on how to make the history logging of the drive? I'm planning to have an S7-300 PLC system with WinCC Runtime for PC based logging.

Hope somebody can suggest...
 
Some newer drives now have real time clocks. That allows a time stamp for faults and alarms in the fault log. Some even take a snapshot of the main drive conditions at the time of fault to assist in troubleshooting.

I don't know if the DanFoss drive has those features.
 
Hi there
You need to study the PKW,PZD area of this drive w.r.t PPO type.
Here you will receive status of the drive like fault mode or warning mode.
You receive the status word at first word of PZD.And by reading a particular bit of the the status word you can learn whether drive is in Fault mode or in warning mode.Which bit of the status word corresponds to fault, warning etc you need to refer the manual of the drive.
If drive stores the alarm Number in a particular parameter, then by linking that parameter to different words of the PZD you will be able to display exact alarm number too.

For displaying time you can use RTC of the PLC.

I danfoss PZD is refered as PCD.
All this assuming you are using profibus to communicate with the drive.
 
DickDV said:
Some newer drives now have real time clocks. That allows a time stamp for faults and alarms in the fault log. Some even take a snapshot of the main drive conditions at the time of fault to assist in troubleshooting.

I don't know if the DanFoss drive has those features.

Danfoss Drives have this feature but for the other models which is for HVAC and WATER applications. Danfoss FC302 does not have real-time clocks and is not expandable to have realtime clock modules.

Thanks
 

Similar Topics

Hello! First post here! Trying to commission a Danfoss FC302 frequency converter (with option A MCA121 EthernetIP-card) connected to ABB AC800M...
Replies
3
Views
1,252
Im working with Danfoss fc302, i got a simple problem inyet icant fixed it, can you help me, we had several drive in our project, to be able...
Replies
2
Views
2,011
Hello, At the company where I'm working for they have standard FB's for controlling FC302 drives. When we do not have a signal to the PLC from...
Replies
1
Views
2,024
Hi, I have a small danfoss FC302 VSD giving a Mech brake low [A63] alarm once or twice a day for some reason. There is no brake and the only I/O...
Replies
14
Views
7,354
Hello, I'm using a Danfoss drive FC302 connect via profidrive to a Siemens PLC 315. My problem is how can I read from the drive a current upper...
Replies
3
Views
2,185
Back
Top Bottom