The deadband concept in AB analogic modules

buhnen

Member
Join Date
May 2008
Location
Somewhereland
Posts
131
Hello everybody,

Just a simple question... As showed in the picture: If I set my alarm deadband to 136, does that means that I'll get two symmetric deadbands High and Low like...


normal operating range from 25839 to -25839

AND

high deadband between 25839 and 25703

AND

low deadband between -25839 and -25703 ?

(25839 - 136 = 25703 ; -25839 + 136 = -25703)

Might it be possible to set an alarm deadband asymmetrically for the Low and for the High?

Thanks in advance

deadband.jpg
 
You are spot on with your deadband calculations:-

High Alarm ON at +25839, OFF at +25703
Low Alarm ON at -25839, OFF at -25703

You cannot set the deadband control at different values for the two alarms in the module configuration, but you could use deadband control in logic instead, by using zero deadband in the module, and by inspecting the data directly.

OTL a new High Alarm bit with GEQ +25839, OTU it LES +25703 *
OTL a new Low Alarm bit with LEQ -25839, OTU it GRT -25703 *

Use you own different values for the OTUs as indicated * above
 

Similar Topics

Hello, I am attempting to tune a PID loop on a process. The process involves a valve with electronic actuator that has quite a high deadband...
Replies
10
Views
2,190
Hello I have alarms that hover around the setpoint to alarm into our control room. To keep from having dozens of alarms. I read we’re the...
Replies
2
Views
1,377
I have several 4-20mA inputs coming from all over the plant into a RA ControlLogix system. Many of these are going into totalizers, being...
Replies
1
Views
1,698
Hi Guys, I have an existing PLC that has a PID that controls a valve that maintains a constant opposing thrust force (in order to keep bearings...
Replies
11
Views
3,250
Hello again! so the PLC I programmed was installed and tested and ready to run the chiller. The rep from Johnson Controls came up and discovered...
Replies
9
Views
9,030
Back
Top Bottom