One of our service guys in the field hooked-up several pieces of equipment via profibus (Siemens S7-300 master). He's having problems communicating and I found out he did not daisy chain the profibus connections. I told him this was wrong, but want to make sure. Must the connections be daisy chained?

(Unfortunately, I think I already know the answer)

Thanks.
 
I have seen that done before, and I think that it ought to work, despite it doesnt look exactly pretty.

I guess he may be a little ignorant about how to make the cable connections.
Try to make it the normal way, and be sure that terminations are ON at the cable ends.

If it still does not work, the most typical beginner error is that the actually used configuration doesnt match exactly the programmed configuration.
If it still does not work, then investigate the HW Diagnostics on the master CPU.
 
Also do not forget to terminate on both ends of the network. Further more there is an 'in' and 'out' for each connector. Make sure that you use the 'in' at both ends.
 
I often recommend going to the http://www.profibus.org web-site - home of the Profibus Organisation. In the "Downloads" section you'll find an Installation Guide. Use this as your bible. If you do this bit correctly and the equipment still doesn't work, then challenge the equipment manufacturer. If his equipment doesn't work when installed according to Profibus Org's rules then what's he going to do to fix it. The stuff is either Profibus-compatible or it isn't. (Of course you might need to double or triple check your wiring first to make sure you're compatible ;) )
 
Pigggy backing at the PLC is fine. Let's say you have ten node. There is no problem making two branches with five nodes originating at the PLC. I've done and seen it many times, and avoids the use of a repeater when you want to have two physical chains due to equipment layout.

Take a look at the terminating resistors at the PLC end. If I remember right, one may have to be on, and one off, but I am not exactly sure.
 
So, if they are piggy-backed, the one on top would be off, and the one connected to the PLC would be on? I never wrote it down when I actually did it, but I seem to think they were of opposite states. I could be wrong though.
 
To my logic they must both be off.
The cable doesnt end at the "piggy-backed" connector. The cable goes in at one connector and out by the other connector.

If the baudrate is 187.5k, you can often get away with wrong terminations. At 1.5M and higher terminations absolutely must be correct.
 

Similar Topics

I am trying to get my S7-315, a TP1200 Comfort Panel, and another profibus device to all communicate. I am using S7 V5.5 for the PLC and TIA for...
Replies
14
Views
3,281
Hey all. I don't like to do this, but we've got like a huge thing going on here, and they'd like for me to get it over with as soon as possible...
Replies
11
Views
5,418
Hello All, I tried searching for this information first, but didn't find anything that helped me out. I'm 99% sure I know the answer, but would...
Replies
2
Views
1,546
I am building a new panel with a GE Versamax PLC and 6 ABB freqdrives, among other things. The powers that be have decided to control all 6 drives...
Replies
3
Views
5,860
Could someone tell How the bits are mapped in a S7 224 For Profibus communcations. I have several that communcate with TI 505, In the s7 software...
Replies
1
Views
2,106
Back
Top Bottom