While researching this new problem, I thought I would ask here since this is better than any knowledgebase.

I have a system that has 2 SLC 5/04 on DH+ at 56K (nodes 1 and 2). There is a message (MSG) from the processor on node 2 to node 1 that send 1 word. This is connected to a DH+ card in a contrologix gateway that is connected to our computer thru an ethernet card that gathers some information from both processors. System has been in place and working for 10 years.

I got a call from my tech on the floor saying that when he went to connect to the processor, he got an error saying target device is not a slc processor. I opened my RSLinx (2.50) and saw the processor dropping offline every 5 seconds then coming right back. Last time I saw this it was the terminating resistor (it is at the end of the line). Changed the resistor and no difference. Ran a new blue hose on the floor and still the same problem. Put the old system back in service and decided to research this a little.

Anyone experience this before? I will post more as I try to fix this.
 
Problem solved

I hate to answer my own post (it's like talking to yourself) but I did get this fixed.

I found the MSG instruction had an error in it (but no error bit set) that was code 37. Answer ID 18352 gave a long list of things to check for - most of which I already checked or eliminated.

The one that fixed it was the FRN of the processor. I was running FRN 3 and the tech note said I needed to be above 5. Since I did not have a flash upgrade, I just installed a new processor with FRN 7.

This has fixed all the problems.

I have over 8 of these little networks (similarly wired but not exact) all running the same FRN on the SLC 5/04. After looking at them, I did find one that was exhibiting the same symptoms but not causing any problems right now. I will try to get a flash upgrade and verify that fixes the problem and it wasn't just a bad processor ( you never know, it could have lost a couple of bits ).
 
While researching this new problem, I thought I would ask here since this is better than any knowledgebase.

I have a system that has 2 SLC 5/04 on DH+ at 56K (nodes 1 and 2). There is a message (MSG) from the processor on node 2 to node 1 that send 1 word. This is connected to a DH+ card in a contrologix gateway that is connected to our computer thru an ethernet card that gathers some information from both processors. System has been in place and working for 10 years.

I got a call from my tech on the floor saying that when he went to connect to the processor, he got an error saying target device is not a slc processor. I opened my RSLinx (2.50) and saw the processor dropping offline every 5 seconds then coming right back. Last time I saw this it was the terminating resistor (it is at the end of the line). Changed the resistor and no difference. Ran a new blue hose on the floor and still the same problem. Put the old system back in service and decided to research this a little.

Anyone experience this before? I will post more as I try to fix this.

You mean at each end of the line right?
 
You mean at each end of the line right?

No, I mean the last time I saw a processor dropping offline and coming back repeatly, it was the last processor in the line and the resistor was not installed. It only affected the last processor on a data highway system with 7 total nodes.
The other end had the resistor and no other unit was exhibiting problems.
 
Last edited:

Similar Topics

Hello and wanted to post for the first time since I just can not figure out what is causing the Ethernet to drop out on 5/05. It all started on...
Replies
0
Views
1,615
I’m attempting to send a temperature from a SLC-5/02 to an EZiMarquee display. The vendor said to use a MSG instruction to send the data to the...
Replies
1
Views
81
Hello all. I have a few SLCs in my plant and of late we've seen a weird issue: The system will be running normally and then randomly the outputs...
Replies
2
Views
93
I am working on setting up a Prosoft Datalogger model PLX51-DLplus-232. This unit will be collecting data from a SLC 5/05 on the DB9 port set to...
Replies
3
Views
103
I have a redundant ControlLogix being set up. This program reads a value from a remote site which happens to be SLC PLC. Rockwell mentions SLC...
Replies
2
Views
95
Back
Top Bottom