Compactlogix L31 unexpected com error during upload

JApt

Member
Join Date
Dec 2008
Location
Maryland
Posts
4
I am having "unexpected communication error" during the upload process. I am using a 9300 USBS, usb to serial converter which will not auto-config. After I manual set up, I can connect with the L31 and begin uploading without issue. I watch the packets in RSlinx diagnostic and when they get to about 1800 sent and received, I get the above error. This always seems to happen during the uploading of the mainprogram tags....well the uploading in general takes forever, but it slowly makes its way through until the com error. I am using version 15 RSLogix 5000 and Version 2.52 RSLinx Classic.

If anyone can help, I would greatly appreciate it. Need more info in order to help me, let me know.

Thanks
 
Thanks Mickey,

We use allot of compactlogix plc's..some of them older than the L31 I am having problems with now. Would I have any problems just upgrading to Ver.17 RSlogix5000? Wouldn't this solve problem?

Thanks
 
Couple problems,

First, re-read the link Mickey posted. RSLogix5000 V17 is OK for offline use only with Windows XP SP3, because but RSLinx is NOT OK with SP3. So, upgrading to V17 won't make everything OK.

Second, if those older processors include 1769-L20s or L30s, the newest firmware for those is V13.
 
Thanks....I may show my ignorance now, but here goes....if the newest firmware for L20 and L30's is V13, then V17 should include all priors versions along with V13 correct? Or now am I confusing firmware versions with RSLogix5000 versions....Sorry...
 

Similar Topics

I'm wanting to upload the program from a CompactLogix L31 Controller. I'm using a generic (non Allen Bradley) "C2G brand" usb -->rs232 cable...
Replies
4
Views
2,853
Hello, I acquired 5 AB Compactlogix racks with L31 processors. The processor batteries had been disconnected. I have not been able to establish...
Replies
6
Views
2,527
I have a compactlogix L31 processor and DigiOne IAP module which I am trying to set up comms with via ethernet. The processor is connected via...
Replies
0
Views
1,878
I’m having a problem connecting with a 1769-L31 Compact Logix Controller It starts to upload and stops midway saying there is a connection error...
Replies
17
Views
5,441
Hi,great site , good to see people taking the time to help others ! I am using a compact logix L31 plc , have used this plc before but have...
Replies
3
Views
3,195
Back
Top Bottom