First thing first -- you desperately need to add some documentation to that program!!!
Then, I think the major problem is that you need to scale your input. You're telling your PID in rung 76 that its setpoint is 120, which appears to be a scaled value. The PV is 4440, which is a raw value that is way out of the bounds that you have configured in your PID.
The reason the output is 6242 is because the SCL destination is being overridden in run 78 because the value is out of range.
All of your PIDs appear to have this same issue.