I would like to network some distributed SLC5/03 processors using only DH485. I was wondering if I can use 1747 NET-AIC interfaces at every SLC to link them to the single DH485 trunk, instead of using 1747-AIC couplers. Is it still a good idea?, I just want to keep them isolated for the DH-485.

DH+ and Ethernet are not options for my application.

If anyone can advice or has had previous experience with NET-AIC for isolation, thanks for any advice !!

Thanks again.
 
Did you mean 1761-NET-AIC's instead of 1746-NET-AIC's?

We use the exact network structure in our plant. We've got 5 or 6 SLC 5/03's each with an RS232 cable going to the AIC+ (1761-NET-AIC) which gives them all connectivity to the main-network, while they all maintain an internal DH-485 network using the other communications port.

The main-trunk as you described it, does get pretty slow though.

Hope this helps,
-Dave
 

Similar Topics

I have an allen Bradley system in which there is two micrologix 1200 and two panel view 300 and a Rsview 32 connected on DH485 network with the...
Replies
2
Views
1,771
Hi, i am trying to create an DH485 netwrok which will consist of 2 ML1500 using ACi units for data acquisition back to a pc. i understand how...
Replies
5
Views
1,989
Hello All, I am currently troubleshooting a communications issue regarding a DH485 network. The network contains PLC1, PLC2, and PLC3, all AB...
Replies
3
Views
3,782
So I am attending a site next week that is reporting PLC communication issues between its three SLC 5/03s (PLC1, PLC2, PLC3). PLC2 communicates...
Replies
3
Views
1,787
Hi, I want to know if and how i can bring up my DH485 network to a ethernet/ip. My network is setting with 1747-aic and 1761-net-aic. So i...
Replies
4
Views
2,284