How can i control a motor dampre with analog output signal from plc?
(plz defind qw to motor damper)
i want to have variable air flow with channging tempreture
 
I don't know what 'qw' is.

I'd say the easiest way is to drive the damper with a damper motor that has a 4-20mA input.

Use a temperature sensor as input to the PLC and vary the position of the damper by PID, if it's a setpoint, or by comparison or look-up if air flow has arbitrary control points.

If you don't already have the PLC, single loop controllers do this as a package, presuming you want to control temperature to a setpoint (which might not be the case).
 
I don't know what 'qw' is.

I'd say the easiest way is to drive the damper with a damper motor that has a 4-20mA input.

Use a temperature sensor as input to the PLC and vary the position of the damper by PID, if it's a setpoint, or by comparison or look-up if air flow has arbitrary control points.

If you don't already have the PLC, single loop controllers do this as a package, presuming you want to control temperature to a setpoint (which might not be the case).
when outdoor air tempreture becomes 24 c or lower the economi9zer system shall be actived. in the case , the fresh , return and exhast air damper shall be proportionaly controled by mixed air tempreture sensor(pt1000)to achive mixed air tempreture sensor wich is 17 c.
at first how can i defined %qw0(analog output to motorize damper)?
i think %QW0:= A (%MW0)^2 + B IN THIS CASE MW0=IW0 AND IW0 IS ANALOG INPUT FROM PT1000
IF THAT RIGHT HOW CAN I DETERMINE A AND B (CONSTANT VALUES)?
my plc is twido (tele) and my motorize damper is siemens
 
when outdoor air tempreture becomes 24 c or lower the economi9zer system shall be actived. in the case , the fresh , return and exhast air damper shall be proportionaly controled by mixed air tempreture sensor(pt1000)to achive mixed air tempreture sensor wich is 17 c.
at first how can i defined %qw0(analog output to motorize damper)?
i think %QW0:= A (%MW0)^2 + B IN THIS CASE MW0=IW0 AND IW0 IS ANALOG INPUT FROM PT1000
IF THAT RIGHT HOW CAN I DETERMINE A AND B (CONSTANT VALUES)?
my plc is twido (tele) and my motorize damper is siemens
You have just described a standard AHU (air handling unit) with economy cycle and OA lockout. There are many DDC or BMS or even standalone controllers already progammed for this, might save u time & money.
 
you have just described a standard ahu (air handling unit) with economy cycle and oa lockout. There are many ddc or bms or even standalone controllers already progammed for this, might save u time & money.
i know that. But I have to use plc because i use plc for other action too. For example change over and .....
 

Similar Topics

How can i control a motor damper with analog output signal from plc? (plz defind qw to motor damper) i want to have variable air flow with...
Replies
1
Views
1,991
We have a damper motor which we need to test. However the method of connection has eluded us. Can any body identify the makers symbol in the...
Replies
10
Views
2,345
We have an application where an operator needs to move an idler roll assembly up and down an incline of about 45o. This will be a completely...
Replies
13
Views
4,683
Can anyone here help me out by identifying this (old) damper actuator motor? Thanks!
Replies
6
Views
3,501
Hello, It is mandatory to use VFD IF i use IE5 electrical motor? What happens If connect it directly as delta without VFD? Please look at motor...
Replies
1
Views
136
Back
Top Bottom