I need an output on a controllogix card to turn off if for whatever reason the PLC fails. The off state of the output enables float control of various sump pumps in a plant. During normal operation these pumps are controlled by the PLC based on milltronics level readings.

What is the best way to determine if the PLC has failed and subsequently turn off the failure output? Using logic to do this doesn't make sense to me as if the PLC has truly failed, all logic should stop executing and therefore the output will remain high.
 
You can configure a fault routine that runs before the PLC shuts down, in this routine you can set the outputs to the desired state. However, I suspect that all outputs go false on a fault.
 
If the Clogix CPU owns the output and the CPU drops out of run mode, the output points owned by that processor should go to their fault states. I believe each point on a Logix output card has a configurable fault state.

The fault states are programmed in each card.

Try going into the properties of the output card in the I/O tree and look for a fault tab which has all of those options.

Paul
 
As Paul suggested, on the Configuration Tab of Module Properties, you can specify Fault Mode states.

I wonder though if this covers all circumstances.

If the application is pretty critical, you might consider an external watchdog timer circuit. The PLC would operate a scheduled task to cycle an output, at say 1Hz, to an external timer relay. The relay remains energized as long as the input pulse from the plc cycles as expected.
 

Similar Topics

I've been called to a site to assist with an ASi fault. The line has been down for a couple of weeks following a failure of the ASi power supply...
Replies
6
Views
1,292
I am looking at an application where I will need to detect small hairline cracks in stamped metal parts. The sensing will need to be done in the...
Replies
10
Views
1,115
Hello everybody, I am working on a project which has HMI FTView SE 13 (Local) and controllogix L71 PLC. I have a question how does PLC detect a...
Replies
0
Views
509
So, we have one servovalve that is very critical to machine operation and idea is (or was) to detect if valve gets disconnected from analog output...
Replies
11
Views
2,870
I had bought a used PLC before but I had to return it. Once in a while its run mode shut off momentarily. I had the PLC on my desk. (No I/Os...
Replies
22
Views
5,352
Back
Top Bottom