milldrone said:
So periodically the PLC shuts the ball valve and looks for the pressure switch to be made.
Just a word of warning for others who may read this thread and thinks about closing the outlet side of a diaphragm pump !!
Don't do it on anything other than an air-operated diaphragm
Mechanically-driven diaphragm pumps are "positive-displacement" meaning that there has to be somewhere for the material in the reducing cavity to go, and if that is closed off, something will "give" (i.e. Break).
Best practise for any P.D. pump application is to have a pressure-relief device, from outlet back to input, in the event the outlet piping is closed-off.
It is also common to put an accumulator bottle on the outlet of a diaphragm pump to smooth out the pulsation of the flow, especially on blending applications. If that is the case, the pressure switch idea probably won't work.
I would go for detection of flow in the outlet. I have in the past used a small and simple "vane" flow detection device. This had a rotor with a magnet in, and a reed switch or hall-effect sensor to detect rotation of the vane wheel. A small bleed flow (using 6mm poly line) was taken from the main flow, through the flow sensor, then back into the main flow. Each stroke of the diaphragm pump would cause the vane sensor to rotate, and I could easily detect the pulses with the PLC.
OkiePC said:
We put a limit switch on them that should change states within a couple of seconds ....
Detecting the diaphragm movement does not indicate the pump is actually pumping anything.