Hello
I would like to connect an load cells 4 or 6 wire to an analogue input EM231.
I don’t want to use SIWAREX MS module .

-------- ------ ---
| | | | | |
| CPU226 |-| EM231|-- ? |- load cells
| | | | | |
-------- ------ ---
I don’t know if I need a transducer
please help me
 
If you do not use a MS module you will have to use a converter to take you load cell signal and convert it into an analog signal. Note: Some resolution will be lost. Amount depends on your analog card and your converter.
 
A method that retains accuracy and resolution is to use an amplifier with an RS485 output like this one. Then use one of the Ports on the PLC in Freeport mode.