I'm trying to test the inputs, basically forcing the inputs ON and seeing if the corresponding lights turn ON on the input module.
Even though the force is accepted, the light on the input module does not goes ON. It should, right?

Any clues are welcome!
Thanks!
 
Actually, no. The LED on the input card simply tells you that the input card senses voltage at the input point and is passing that information to the CPU.

An input force is only affecting the input "image" or data table of the PLC. Input forces effectively bypass the input card and its LEDs. The purpose of an input force, is to make the program believe that a particular input point is in a particular state, regardless of what the input card "thinks".

Now, an output force is different, because forcing an output actually does intend to cause the output point to turn on, and the output image including the force, will get copied to the output card and cause the LED to illuminate.

EDIT: To actually test the inputs, you should apply the proper signals to them (with a jumper wire for example) and watch the LEDs and, more importantly, your programming software for a change of state at each point.

Paul
 
Last edited:

Similar Topics

Good Morning , I upgraded a machine a few weeks ago . To continue making improvements without shutting down the machine , I would like to...
Replies
6
Views
2,156
Good Morning , We have a shelf of ControlLogix and Compactlogix CPU's . I would like to test these and also use these for training . Can you...
Replies
2
Views
1,719
I am trying to test a scanner application where I am converting RS232 to Ethernet IP, and then reading the results at an A-B compactlogix L23E...
Replies
5
Views
3,376
I am working on setting up a Prosoft Datalogger model PLX51-DLplus-232. This unit will be collecting data from a SLC 5/05 on the DB9 port set to...
Replies
3
Views
103
Hi all, I have a AC current transducer that I want to bench test to ensure I am getting a 4-20mA output. I am using a AE001 unit. It is very...
Replies
4
Views
119
Back
Top Bottom