I used to work at a plant that had all honeywell DCS systems and used loop power on 90% of their transmitters. The plant close for lack of business and now I have found myself in a plant using mostly PLC 5's. I have been ask to install 3 loop powered level transmitters but I'm not sure if it can be done using a PLC. On the DCS system the module sent out 0 to 24 volts DC to the transmitter. Based on the resistance of the measuring device it would drop the 24 volts to somewhere between 0 to 24 volts or 4 to 20 milliamps. You would then scale that value. How would I use loop power 2 wire control using the PLC 5. Do I need a special module that would sent out the loop power on one pair and then read back from that module and input value??? The particular device that I am installing is a 5303HA1S1V5AE0200RBE5M1 = $2937.60 from the website Website: http://www.emersonprocess.com/rosemount/products/level/m5300b.html
I would appreciate any help that you guys could give me!!

Thanks
Tommy
 
Loop powered instruments are quite common on the PLC-5. The difference is that on a DCS you typically just wire it up to the termination assembly, on a PLC you have to include the power supply in your loop. If you get the AB manual for the I/O module you are using, they have typical wiring diagrams. Another difference is that DCS systems usually have isolated channels, in the PLC-5 you can have differential (isolated) or single ended (all the transmitters share a common). Again, this is covered in the I/O module wiring diagrams.

Post your I/O module and we can help. Also scaling in a PLC-5 is much different than what's done in a DCS, there are no AIN blocks or such. You will most likely use the Compute instruction, within a ladder.
 
The DC power supply that you use for you transmitter should not be the rack mounted power supply that powers the PLC-5 rack.

Transmitter power is supplied from an independent power supply, typically 24Vdc.
 
Good advice from Ken Moore & Danw. Don't forget to add some circuit protection, e.g. 1/4 Amp fuse or breaker for each loop with a 1 Amp supply. Don't oversize the protection, a half amp fuse might never blow with a 1 amp supply, just pull the Voltage down.
Roy
 

Similar Topics

Complete noob here, using a Click C0-02DD1-D to run a test stand. Requirement is to turn on motor run for X seconds, turn off and dwell for X...
Replies
6
Views
1,062
Good Day everyone I am currently writing a program for a 4 cylinder press i have it mostly done. just have one issue with my program where i...
Replies
18
Views
3,921
Good Evening , I’m getting ready to integrate a Mettler Toledo IND 570 into a ControlLogix PLC , Analog 4-20 ma input card 1756-IF16 . I’m...
Replies
6
Views
2,291
Hello to all, I have an application where I have one transmitter 4-20 mA (loop powered) and I need to connect its current output to two AI...
Replies
9
Views
2,826
Dear Dox 10 Gurus, I actually have very limited knowledge about dox 10 and I d like to consult you about attached error. I have a program and I...
Replies
1
Views
1,458
Back
Top Bottom