Hello

i have two question. will an ab panelview plus retain it alarm history when power is disconnected from it? Also i am using a compact logix controller (L32E) and a 1769-HSC card in slot one. the card is working but i can not get the output to activate, OTE(Local:1:O.Ctr0En) is always on and so is OTE(Local:1:O.OutputOffMask.0). please help
 
In answer to your first question Jim, then YES, the PV+'s 'should' retain alarm history, as long as you have not ticked various option in the terminal settings to 'Delete log files' (or similar).

We have just had a case though where a PV+1500 had a corrupt internal flash card (according to tech support) - and so was doing just that...(losing alarms/alarm history on power up)

Hope this helps.


Rob
 

Similar Topics

TN10529 Hi Im a customer first but for some reason cant access on my account Can someone please give me the above tech reference i think it will...
Replies
2
Views
1,622
Hello Friends, I am beginner in Siemens PLC programming. Can anybody guide me do we have Tech Support Help(Chat Or Call) for Siemens PLC(S7...
Replies
2
Views
2,748
Hello, I am trying to get a 32MV4341 Lenze AC Tech VFD running a conveyor to be controlled by a 24VDC photo eye on the nose end of the conveyor...
Replies
3
Views
1,924
I am having an issue with a (no longer supported) Toshiba EX-100 PLC. The problem started with an external wiring short that shut down the PLC...
Replies
3
Views
2,004
  • Poll
How many people here give to the local tech schools? I am a member of the advisory board for the electronics department at my local tech school. I...
Replies
46
Views
9,595
Back
Top Bottom