AB PV550 Firm ware questions

glpdrumerx

Member
Join Date
Oct 2006
Location
Tennessee
Posts
48
I am installing an AB panelview 550 and can't seem to communicate with it I've tried going thru a slc 504 and also direct connection thru the com port but am having no luck. I have logged on to other machines to make sure I can communicate to other plc's and panelviews and that works. Could the firmware verson cause a conflict? that is the only difference I have seen.
 
Your PV has a RS232 port with DH485 protocol. If your PC has a real serial port then use a straight thru cable and the 1747-PIC/AIC+ driver in RSLinx to communicate with the PV.
If you do not have a real serial port the the 1747-UIC ( USB to DH485 converter) will be needed to connect.

You could use a passthru connection thru your SLC5/04 ( DH+ to DH485).
You would need to connect to the SLC's DH+ port then passthru to the serial port configured for DH485. Processor would have to be configured for passthru comm. Of course extra hadware is required to connect to the DH+ port.
 
Last edited:

Similar Topics

Is there a way to add a stop to the attached program? I want to stop it after the first rinse so the operator would have to push a button for it...
Replies
10
Views
1,221
I'm trying to connect a PV550 (2711-T5A2L) to a 1761-NET-AIC using a 1747-C11 cable (w/RJ45 removed) and the Phoenix connector. Can someone tell...
Replies
8
Views
2,662
We have an old machine that has been mothballed since early 2018 and management are looking at more work for it in 2022. The system runs on an SLC...
Replies
12
Views
2,854
Trying to write a program for a PV550 (2711-T5A16L1, Ser. B, Rev. E, FRN 4.46) to test the touchscreen. I wrote a program with 16 pages and on...
Replies
2
Views
1,690
Good Morning Folks. Win Xp, PRO, Version 2002, SP3 RSLinx Classic 2.54 Using the AB UIC-485 driver with the 1747-UIC and a 2711-NC13 connected...
Replies
1
Views
1,217
Back
Top Bottom