Hello, I am converting a DL-305 program to DL-205 manually run by rung. No problems with the I/O, timers and counters etc.

Question#1: The 305 uses "SR" for the state relays and the 205 uses "S", Are they handled the same way? (besides the range)

Question#2: The 305 uses MCS and MCR and the 205 uses MLS and MLR, the MLS and MLR have a "K" value, It says that the "K" value is used when nesting MLR and MLS. I am not nesting but the MCR,MCS in the original program is used multiple times, Do i use the MLS K1 and MLR K0 multiple times without changing the "K" value?
Thanks

dl6.jpg
 
1. The SR bits were Shift Register Bits. Memory allocated specifically for Shift Registers. You should replace these with standard C coils in the 205. The S coils are Stage Bits. Totally different function, although you could use them in a shift register. Don't forget they have to be on 8 bit bounderies(ie. C0-C7, C20-C37..etc)

2. Yes, the K value only increases when you nest to inner levels and decreases when nesting out. So if you are not nesting anymore than 1 level at a time, you would have MLS K1 and MLR KO mulitple times.
 
Last edited:
Thank you ATU...

Changing the SR bits to C coils looks like it should do the trick.
Why there are SR bits when there is no shift registers in the program is unknown to me. This program was written for a GE Series One PLC with Logicmaster 20+ years ago and converted to DirectLogic when a new CPU was installed.
 
Was the program short on internal bits? Memory is memory. Maybe the programmer ran out of internal coils?
 
The program is not long for todays standards, the original cpu was a ge series one 101 and was upgraded to a DL-330 to get more memory for a machine upgrade, then it was upgraded to a DL-340 when the DL-330 died.
The original program has been modified and band-aided many times over the years. So yes it could be a memory issue.
 
Conversion complete, back in business.
In the 305 you can use SR as a normal internal coil as long as there are no shift registers in the program as in this case.
Thanks again ATU.
 

Similar Topics

Hello, I have an automation direct d2 262 plc and C-more HMI EA9T6CL-R. I need to prepare a program, scheduled to be performed on a future date. I...
Replies
1
Views
27
Hello all- I have a unique challenge using a customers Direct logic 06 PLC. This customer has a DC motor operating at 10 RPM which is turning a...
Replies
1
Views
88
Hi, I have been trying to run drive via Sysmac studio. I can ping the drive. I can see the logic bits going on/off as per command. But, drive is...
Replies
21
Views
469
Anyone tried Automation Directs new CM5 HMI. We've been the EA9's for a few years now with minimal complaints. A few failures here and there but...
Replies
17
Views
1,418
I'm using an Automation Direct GS20 VFD for the first time and I have a question for the Automation Direct gurus regarding the recommendation of a...
Replies
2
Views
1,064
Back
Top Bottom