I have a Heindenhain Eencoder ERN 480 1024 IMPULSE.
The ECO servo drive fault number is F249 =" Check encoder and encoder cable"
Using my fluke meter I checked for cable continuity from one end to the other.
The cable have 8 wires.
How Can I test this encoder?
I'm also looking for a cable and encoder data sheet.
I searched on the net. But is not clear to me the 1Vpp 1024
Is there a direct replacement encoder that I can buy at McMaster catalog that I can use without without having to mess with the ECO servo drive?.
I thank you in advance for your help and education.
 
the simplest answer is "it depends". what is the output type?
according to this, it may be sin/cos:
http://www.auto-met.com/heidenhain/rotary_encoders/rotaryencoders/ERN/ERN400.htm

the easiest is to use an oscilloscope and look at outputs while slowly (really slowly) turning the shaft. if it is quadrature (pulse) encoder and this goes to plc high speed counter card, you can also look at the input LEDs.
 
I have used a scope to check an incremental encoder.
It checked out fine BUT if you put any perssure on the drive (It was belt driven) it stopped working!
Fixed with a new one!
 
If the ECOdrive is fitted with a Heidenhain, replace it with same. If you've tested the cable, that's about all you can do in the field. I'm guessing you could buy a special tester, but, at the end of the day, a replacement encoder is likely cheaper to buy, and likely the root of the problem. If you go down the 'couldn't I buy it cheaper from a catalog?' route, you'll also void the warranty of the drive, in case you didn't know that.
 
Buying an encoder from a catalog is NEVER a good idea! If you want to ensure that you get the encoder that you need... not the encoder that you want... you should talk to an encoder supplier/manufacturer. They will be able to spec out an encoder that WILL work for your application.

One wouldn't go to a catalog to pick out a wife would they?

DON'T ANSWER THAT!!! lol
 
Never rule out the cable just cours you measured it.
Encoder cables are very fragile and sensitive for EMC and faulty grounding.
 

Similar Topics

Hello, I have a balluff network i/o block, BNI EIP-538-005-z063, and I can't establish a connection with it from my PC or PLC. I tried pinging...
Replies
5
Views
345
Does anyone know of a good person/company that could troubleshoot an electrical problem in a control panel in South Carolina - tomorrow? If...
Replies
9
Views
2,198
My attempt to communicate with Foundation Fieldbus transmitters with Pactware and a new, out-of-the-box Softing FF modem are a disaster - failure...
Replies
17
Views
5,011
Hi, I am dealing with a single SBR subroutine thats handed 1 input paramter UDT P.x multiple times: (Pump) P.1/2/3/4/5. I JSR into the same...
Replies
3
Views
1,989
Hi all, I've been making good progress with the WWTP lightning strike issue, CPU and I/O for the Plant PLC is up and running, and data is coming...
Replies
2
Views
1,778
Back
Top Bottom