Hi all,

I had a engineer move an alarm input from an isolated digital input Card (AB 1756-IA16I) to a regular digital input card (AB 1756-IA16).

He made the change because "the device was supplied with dry contacts for alarm outputs".

I am unable to contact him this week to ask him why he had to do this, so I going to through this one out to the PLCS.net community.

Any thoughts?
 
If the device is using dry contacts as outputs then it is isolated.

Think of it this way. Instead of the isolation taking place on the PLC input card it is taking place on the device. As long as the power used to run thru the dry contact is common to the plc card everything is good.
 
Yes the device would still have worked on the isolated input card, but it would kind of be wasteful because its not using the capability that you specifically get when using an isolated card. Its unnessary to use an isolated card to monitor dry contacts.

If there are other I/O points being used on both of those cards, the engineer may have moved the point from one card to the next just for the sake of functional partitioning.

$
 
thank you

sir please kindly briefly explain me how we can identify which alarm is ringing using plc,

my question was, see i have 10 alarm as input and display which alarm ringed first. which is the medium to recognize which alarm is first because all alarms can ring at a time. please give me your feedback sir. i am new too this plc programming.
 
upendra_sp, welcome to the forum. Mr. Carlton is telling you to start a new question - called a thread. This is better than adding your new question at the end of an existing thread - which is over a year old.

So instead of clicking on "post reply" at the top left of an existing thread, you want to go here:
http://www.plctalk.net/qanda/forumdisplay.php?f=2
and click on "start a new thread", the green button at the top left.

Start a new thread, then ask your question. :)
 
bill tell the engineer it can be a safety issue now. The alarm will not be activated when any short in the line. So that is why isolated is used.
I do know it is easier and cheaper to use not isolated, however it has drawbacks.
or he does not have correct card with him.
just ask the man.
i do same btw as problems have to be solved.
 

Similar Topics

Off topic, but you people here usually have pretty good suggestions. Title kind of says it, anyone know of a DC current switch that has a decent...
Replies
1
Views
737
I've used Banner for RTD's, thermocouples and 4-20's but not for discretes. I called the factory to find out whether either PNP or NPN wiring...
Replies
1
Views
1,469
How much current flows typically through a dry contact to a digital input module? Using 120VAC module and power. I'm assuming around 30mA. I'm...
Replies
3
Views
1,566
Dear, I was wondering which one is better to use a PNP sensor or a dry contact sensor, I was checking the inductive sensor from Schneider...
Replies
10
Views
3,748
I would like a NO VOLTAGE, DRY CONTACT proximity switch. Give me one now! Or please direct me to a website where I may purchase one or make...
Replies
8
Views
5,175
Back
Top Bottom