I am interfacing KS800-DP modules (temperature controller made by PMA) with SIEMENS S7-317 2DP CPU, using PROFIBUS DP Communication.
The GSD file for the KS800-DP is installed and the hardware configuration is ok.
But the problem is with the “Process data” communication: I am unable to read and write values in sequence using SFC14 and SFC15. I cannot be read with the same SFC14 more than one byte. I have to call SFC14 each time for every byte alone.

I tried another way: read/write directly in the peripheral memory, but also it is working for each byte alone.
The telegram to transfer the process data is really long (66 bytes inputs and 52 bytes outputs), and I do not want to write a line for each byte (I have 5 controllers!).
Is there a way to use pointers to access these data sequentially?

Thanks
 
SFC14 and SFC15 should work with 3 bytes or 5 bytes or more.
1, 2 and 4 bytes shall be accessible with regular i/o addressing.

So it makes very little sense that you cannot get it to work.

How does your code look like ?
What is the status message from SFC14 or SFC15 ?
 
the PMA have specific data types (some are bytes, others words or dword,...). this means that if the transmitted data type is word, we cannot read it as byte or 4 bytes, only as 2 bytes.
so we tried to do indirect addressing as follows, and now it is working ok. thank you anyway.


input
L P#256.0 // load PIW 256
LAR1
L PIW [AR1,P#0.0]
T MW xxx ( DBxx.DBW xxx) // Transfer to xxx



output
L P#256.0 // transfer to PQW 256
LAR1
L MW xxx ( DBxx.DBW xxx) // Value for Output
T PQW [AR1,P#0.0]

 
Yes, but i have 5 controllers with 66 bytes inputs and 52 bytes outputs each. So I will have to write hundreds of lines in the program. That is why I preferred indirect addressing.
Thanks
 
Actually, if the inputs and outputs are arranged in large contigous blocks, then I cannot see why SFC14 and SFC15 shouldnt work.

I am guessing that you need to setup all the data from each controller as consistent contigous.
The SFC14 and SFC15 calls must match exactly the consistent contigous data areas.
All DP slaves have a slightly different setup dialog. But I am guessing this setting is in there somewhere.
 

Similar Topics

Could anybody please shed some light as to what are the steps in making a communication between Compactlogix 1768-L30ER CPU and Siemens S7 CPU...
Replies
3
Views
2,695
Hi! I am following this document of Siemens DP/DP coupler...
Replies
0
Views
1,170
Hello, I'm writing my first program for S7-1200 and have some problems with communication between CM 1243-5 and FC302 via profibus dp Is there a...
Replies
2
Views
3,802
Hello all. I have a problem about communication between cpu s7300 and cpu et200. Thanks
Replies
1
Views
2,912
HELLO ALL. I HAVE A PROBLEM about communication between cpu s7300 DP and S7300 CP. THANKS
Replies
4
Views
4,322
Back
Top Bottom