My fearless leader just dropped a knot into my programing for the day..I have to put 3 heater loops (feeding 3 groups of 2 banks) into a AD DL260 ...
Tank #1 Bank A 18 kw Run to Set point
Control Loop #1
Tank #1 Bank B 18 kw Run to Set point < 10 deg
Tank #2 Bank A 18 kw Run to Set point
Control Loop #2
Tank #2 Bank B 18 kw Run to Set point < 10 deg
Tank #3 Bank A 18 kw Run to Set point
Control Loop #3
Tank #3 Bank B 18 kw Run to Set point < 10 deg
The temps are coming in from a AD F2-04THM 4 channel card...
My question is: Can I just set up a compare for each bank and feed that with a setpoint value that I set from the CMORE panel, or do I need to set up 3 (or 6) PID loops to run them?
The tanks are SS, the liquid is water, the cyclic heat demand will be fairly even...once the tanks are up to setpoint, one heater per tank should be able to maintain the load.
Thanks group...My head is just not up to speed today.
David:site::site:
Tank #1 Bank A 18 kw Run to Set point
Control Loop #1
Tank #1 Bank B 18 kw Run to Set point < 10 deg
Tank #2 Bank A 18 kw Run to Set point
Control Loop #2
Tank #2 Bank B 18 kw Run to Set point < 10 deg
Tank #3 Bank A 18 kw Run to Set point
Control Loop #3
Tank #3 Bank B 18 kw Run to Set point < 10 deg
The temps are coming in from a AD F2-04THM 4 channel card...
My question is: Can I just set up a compare for each bank and feed that with a setpoint value that I set from the CMORE panel, or do I need to set up 3 (or 6) PID loops to run them?
The tanks are SS, the liquid is water, the cyclic heat demand will be fairly even...once the tanks are up to setpoint, one heater per tank should be able to maintain the load.
Thanks group...My head is just not up to speed today.
David:site::site: